Modbus SunSpec support - Printable Version +- LogicMachine Forum (https://forum.logicmachine.net) +-- Forum: LogicMachine eco-system (https://forum.logicmachine.net/forumdisplay.php?fid=1) +--- Forum: Scripting (https://forum.logicmachine.net/forumdisplay.php?fid=8) +--- Thread: Modbus SunSpec support (/showthread.php?tid=801) |
Modbus SunSpec support - joost001 - 22.05.2017 Does the modbus implementation in LM support the SunSpec Modbus Profile? I have an SMA invertor for my solar panels that I would like to query using the modbus protocol the parameters in attachment. regards, Joost RE: Modbus SunSpec support - mlaudren - 22.05.2017 If the modbus bus is not proprietary the LM should be able to handle it. You can try with this. Code: require('luamodbus')
mb = luamodbus.rtu()
mb:open('/dev/RS485', 19200, 'E', 8, 1, 'H') -- change with correct MB settings : speed, parity, stop bit, ...
mb:connect()
if mb ~= nil then
value = mb:readregisters(40188) -- read AC current register
log(value)
mb:close()
endRE: Modbus SunSpec support - admin - 23.05.2017 The correct address is probably not 40188, but either 187 or 188. You can check this quickly with RTU test. If you want to create a profile, then address_scale field should be used to tell where to read the scaling factor from. |