Deactivate button - Printable Version
+--- Thread: Deactivate button (/showthread.php?tid=829)
Deactivate button - XSPA2474KW - 08.06.2017
HI to all
I want to press a button in LogicMachine and then for a predefined time, pushing the button for a second, third or fourth time to not activate it.
Example.
First time: Push button 1 (do something and start counting 1 min)
Second time (after 20 sec): Push button 1 do nothing
Third time (after 30 sec): Push button 1 do nothing
Fourth time (after 50 sec): Push button 1 do nothing
Fifth time (after 1min and 10 sec): Push button 1 do again something.
Do you have any identical script?
Thanks for you cooperation!
RE: Deactivate button - mlaudren - 08.06.2017
You could use couple of counter and timer to define time since last push like:
local pushcount = storage.get('pushcount', 0) local timepush = os.time() local timepushinit = storage.get('lastpush', 0) delta = timepush - timepushinit if delta > 60 then pushcount = 0 storage.set('lastpush', timepush) end if pushcount == 0 then  -- do something elseif pushcount == 1 and delta > 20 then  --do something elseif pushcount == 2 and delta > 30 then  -- ... else  -- do something end pushcount = pushcount+1 storage.set('pushcount', pushcount)
RE: Deactivate button - XSPA2474KW - 25.06.2017
(08.06.2017, 10:28)mlaudren Wrote: Hi,
Hi mlaudren
thanks for your reply. I have written the code below but it is not working right. The code is working right at first time once, but when I change the temperature '5/3/0' manually, the Temp is not updated. Can you help?
--Temp=grp.getvalue('5/3/0')
--storage.set('Temp',Temp)
local Temp = storage.get('Temp',0)
grp.write('11/4/1',delta)
--grp.write('11/4/4',ActualTemp)
if delta > 15 then
pushcount = 0
ActualTemp=grp.getvalue('5/3/0')
storage.set('Temp', ActualTemp)
Temp=Temp+0.5
storage.set('Temp', Temp)
grp.write('11/4/3',Temp)
Temp=Temp
--storage.set('Temp', Temp)
grp.write('11/4/2',pushcount)
--grp.write('11/4/3',Temp)
RE: Deactivate button - mlaudren - 27.06.2017
Hi mlaudren
if delta > 15 then
pushcount = 0
   Temp=Temp+0.5
   Temp=Temp
I think you have a mistake in your code.
You read the address 5/3/0 and save the value in 'Temp'
but you never use this value after. so you only increase a value by 0.5 every time you press your button.
Look at the text I put in red.
What do you want to do?
if the user press 1 time, increase the setpoint to current+0.5?
Here is what the code do actually:
Get Temp, delta, pushcount; if delta > 15   reset pushcount; end if pushcount == 0   Get actualtemp from (5/...)   Save actualtemp to 'Temp'   Temp +0.5  <-- it's the variable temp not the same as 'Temp' first time is equal to 0   Save Temp to 'Temp' <-- you override actualtemp you set just before   Write Temp to Addr(11/...) else   Get actualtemp from (5/...)   Save actualtemp to 'Temp'   Temp=Temp <-- What the point to do this?   Save Temp to 'Temp'  <-- same as above, you override actualtemp you set just before   Write Temp to Addr(11/....) end increase pushcount Save pushcount in 'pushcount'
Is it the same subject this question: https://forum.logicmachine.net/showthread.php?tid=866 ?
RE: Deactivate button - XSPA2474KW - 29.06.2017
Hi again
I want to increase the temperature by 0,5 every time i press the button but at the same time delta is > 60.
If I press the button and delta is < 60 do nothing.
Thanks in advance!
RE: Deactivate button - admin - 29.06.2017
Already answered in another topic of yours:
RE: Deactivate button - XSPA2474KW - 02.07.2017
Yes in fact is the same question!