Posts: 15
Threads: 4
Joined: May 2017
Reputation:
0
Hello!
Is it possible to setup a Homelynk as a Modbus slave on TCP/IP?
Regards!
P
Posts: 5588
Threads: 30
Joined: Aug 2017
Reputation:
250
------------------------------
Ctrl+F5
Posts: 15
Threads: 4
Joined: May 2017
Reputation:
0
Posts: 15
Threads: 4
Joined: May 2017
Reputation:
0
Hello!
This works fine in genneral but I have an issue with the temperature. When I set the datatype in the script to float16 I get wrong scale on the modbus side. For example if the temperature value is 7.5 on KNX side I get value 7 on modbus side. I should get 750. If I change the datatype in script to int16 it gets completely wrong because temperature on KNX are float16. Are there any way to integrate a multiplier in the script only for float16 objects?
Posts: 5588
Threads: 30
Joined: Aug 2017
Reputation:
250
You should make the conversion outside the script. Use an virtual object for modbus and make simple event script like this.
Code: grp.update('virtual object address', event.getvalue()*100)
------------------------------
Ctrl+F5
Posts: 15
Threads: 4
Joined: May 2017
Reputation:
0
Hello!
Are there any limitations of the amount of adresses in this script above? Or are there any ather better way if there is a lot of adresses? I have a project where I have a modbus master that have to read about 300 adresses.
BR
Per-Åke
Posts: 1818
Threads: 8
Joined: Jul 2015
Reputation:
121
08.11.2019, 07:59
(This post was last modified: 08.11.2019, 08:00 by Erwin van der Zwart.)
Hi,
Hard to say exactly as it depends on other processes in your controller like amount of KNX object updates etcetera. The indicator of limitations is most of the time the CPU load.
We tested a lot of scenarios / addressable limits and you can see them in this document: https://www.schneider-electric.com/en/download/document/AN017/
On page 13 you can see the results of a test with 1000 objects on a HW2 device (you can increase this on HW3).
So if your controller is not doing anything else then 300 objects should work just fine.
BR,
Erwin
Posts: 148
Threads: 38
Joined: Sep 2016
Reputation:
1
I have a problem with the script..
I have 2 LM:
LM1 is the one with this script https://openrb.com/lm-as-modbus-tcp-slave
LM2 is the one that need to read LM1
When I try to read with LM1 my LM2, LM2 return tis error: LM (TCP 192.168.1.91:502) read failed: Illegal data address
The profile in LM2 is this:
Code: {
"manufacturer":"LM",
"description":"LM",
"mapping":[
{"name":"Reg1", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 0, "writable": true},
{"name":"Reg2", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 1, "writable": true},
{"name":"Reg3", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 2, "writable": true},
{"name":"Reg4", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 3, "writable": true},
{"name":"Reg5", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 4, "writable": true},
{"name":"Reg6", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 5, "writable": true},
{"name":"Reg7", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 6, "writable": true}
]
}
and the script in LM1 is:
Code: if not mb then
require('genohm-scada.eibdgm')
require('luamodbus')
-- Elenco mappature bobine, a partire da 0
coils = { '1/1/1' }
-- Elenco mappature dei registri, a partire da 0
registers = { "1/2/0", "1/2/3", "1/2/4", "1/2/9", "1/2/14", "1/2/16", "33/0/1" }
-- Elenco tipo di dati del registro, il conteggio degli elementi deve corrispondere alla tabela dei registri
regdt = { dt.uint16, dt.uint16, dt.uint16, dt.uint16, dt.uint16, dt.uint16, dt.uint16 }
-- Richiamo in scrittura del gr. KNX
function knxgroupwrite(event)
local value
-- Prova a trovare la bobona corrispondente
for id, addr in ipairs(coils) do
if event.dst == addr then
value = knxdatatype.decode(event.datahex, dt.bool)
mb:setcoils(id - 1, value)
end
end
-- Prova a trovare il registro corrispondente
for id, addr in ipairs(registers) do
if event.dst == addr then
value = knxdatatype.decode(event.datahex, regdt[ id ])
mb:setregisters(id - 1, value)
end
end
end
-- richiama bobina in scrittura
function mbwritecoils(coil, value)
local addr = coils[ coil + 1 ]
if addr then
grp.write(addr, value, dt.bool)
end
end
-- registra la chiamata in scrittura
function mbwriteregisters(register, value)
local addr = registers[ register + 1 ]
if addr then
grp.write(addr, value, regdt[ register + 1])
end
end
-- knx group monitor, gestisce le scritture di gruppo
knxclient = eibdgm:new({ timeout = 0.1 })
knxclient:sethandler('groupwrite', knxgroupwrite)
-- modbus slave, ascolta su tutte le interfaccie e porte default 502
mb = luamodbus.tcp()
mb:open('0.0.0.0', 502)
-- Impostazione Slave (Facoltativa)
--mb:setslave(1)
mb:setreceivetimeout(0.1)
mb:setmapping(#coils, 0, #registers, 0)
-- Inizializza bobine
for id, addr in ipairs(coils) do
value = grp.getvalue(addr)
mb:setcoils(id - 1, value)
end
-- Inizializza registri
for id, addr in ipairs(registers) do
value = grp.getvalue(addr)
mb:setregisters(id - 1, value)
end
-- set callbacks for coil and register write
mb:setwritecoilcb(mbwritecoils)
mb:setwriteregistercb(mbwriteregisters)
end
-- Gestione modbus e KNX
mb:handleslave()
knxclient:step()
can someone help me?
Posts: 5588
Threads: 30
Joined: Aug 2017
Reputation:
250
Why do you need modbus to communicate between two LMs?
------------------------------
Ctrl+F5
Posts: 148
Threads: 38
Joined: Sep 2016
Reputation:
1
17.09.2020, 08:46
(This post was last modified: 17.09.2020, 08:47 by Mirco.)
It is only a test, I need to read from an LM with modbus TCP
Posts: 5588
Threads: 30
Joined: Aug 2017
Reputation:
250
I just tried it like this and it works fine.
Code: if not mb then
require('genohm-scada.eibdgm')
require('luamodbus')
-- Elenco mappature bobine, a partire da 0
coils = { '32/1/23' }
-- Elenco mappature dei registri, a partire da 0
registers = { "32/1/21", "32/1/22" }
-- Elenco tipo di dati del registro, il conteggio degli elementi deve corrispondere alla tabela dei registri
regdt = { dt.uint16, dt.uint16 }
-- Richiamo in scrittura del gr. KNX
function knxgroupwrite(event)
local value
-- Prova a trovare la bobona corrispondente
for id, addr in ipairs(coils) do
if event.dst == addr then
value = knxdatatype.decode(event.datahex, dt.bool)
mb:setcoils(id - 1, value)
end
end
-- Prova a trovare il registro corrispondente
for id, addr in ipairs(registers) do
if event.dst == addr then
value = knxdatatype.decode(event.datahex, regdt[ id ])
mb:setregisters(id - 1, value)
end
end
end
-- richiama bobina in scrittura
function mbwritecoils(coil, value)
local addr = coils[ coil + 1 ]
if addr then
grp.write(addr, value, dt.bool)
end
end
-- registra la chiamata in scrittura
function mbwriteregisters(register, value)
local addr = registers[ register + 1 ]
if addr then
grp.write(addr, value, regdt[ register + 1])
end
end
-- knx group monitor, gestisce le scritture di gruppo
knxclient = eibdgm:new({ timeout = 0.1 })
knxclient:sethandler('groupwrite', knxgroupwrite)
-- modbus slave, ascolta su tutte le interfaccie e porte default 502
mb = luamodbus.tcp()
mb:open('0.0.0.0', 502)
-- Impostazione Slave (Facoltativa)
--mb:setslave(1)
mb:setreceivetimeout(0.1)
mb:setmapping(#coils, 0, #registers, 0)
-- Inizializza bobine
for id, addr in ipairs(coils) do
value = grp.getvalue(addr)
mb:setcoils(id - 1, value)
end
-- Inizializza registri
for id, addr in ipairs(registers) do
value = grp.getvalue(addr)
mb:setregisters(id - 1, value)
end
-- set callbacks for coil and register write
mb:setwritecoilcb(mbwritecoils)
mb:setwriteregistercb(mbwriteregisters)
end
-- Gestione modbus e KNX
mb:handleslave()
knxclient:step()
profile
Code: {
"manufacturer": "Embedded Systems",
"description": "LM11",
"mapping": [
{ "name": "Output 1", "bus_datatype": 1, "type": "coil", "address": 0, "writable": 1 },
{ "name": "Input 1", "bus_datatype": 7, "type": "register", "address": 0, "writable": 1 },
{ "name": "Input 1", "bus_datatype": 7, "type": "register", "address": 1, "writable": 1 }
]
}
------------------------------
Ctrl+F5
Posts: 148
Threads: 38
Joined: Sep 2016
Reputation:
1
what!?  how is it possible?
Can I know how you set objects?
Posts: 5588
Threads: 30
Joined: Aug 2017
Reputation:
250
Like this
Which FW do you use?
------------------------------
Ctrl+F5
Posts: 148
Threads: 38
Joined: Sep 2016
Reputation:
1
17.09.2020, 10:11
(This post was last modified: 17.09.2020, 10:12 by Mirco.)
mmm really strange.. now that I use the same datatype (my fault) I have no error, but I read always 0, no matter what I write into objects..
The FW is 20200116
Posts: 5588
Threads: 30
Joined: Aug 2017
Reputation:
250
Do you use same type objects in both LMs? It works fine in both directions.
Disable and enable the script.
------------------------------
Ctrl+F5
Posts: 148
Threads: 38
Joined: Sep 2016
Reputation:
1
17.09.2020, 10:39
(This post was last modified: 17.09.2020, 10:40 by Mirco.)
ok now it works! I have disable and enable again the script and it start working
|