This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

FB Editor
#1
I found in the latest release 20201210 FB Editor 2.0 the function to calculate a sliding setpoint with or without offset.

I tried it but there seems a bug in the one with offset:

[Image: PU3dB0E.png]
Does somebody also know why the settings are only available as value and not object?
For installers i normally make the X and Y value programmable. For end user normally only the Offset on Y is a settingĀ (but this is also only available as value).
Reply
#2
This is defined in the function which defines this block. Here are all the function https://forum.logicmachine.net/showthrea...49#pid4849. You can import them to user libraries and modify. This is quite old one and not sure if this is same like in the current FB.
------------------------------
Ctrl+F5
Reply
#3
Nope i checked and tested this one has the bug in both. So it seems the curve with 2 points function is updated sometime ago.

with the data above the outcome for both is now -10

Reply
#4
I will try to get updated libs but it was done buy external dev so it might take some time.
------------------------------
Ctrl+F5
Reply
#5
I reverse engineered it and used some excel to test the calculations and the one below works.

--- [Function] fbe_curve_2pt
--- Curve function with 2 points
--- [Comment]
--- Depending on a straight line defined by 2 points, this module supplies a y-value for an x-value.
--- The first point of the straight line is defined by x1 and y1.
--- The second point of the straight line is defined by x2 and y2.
--- If x is less than x1, then y=y1.
--- If x is greater than x2, then y=y2.
--- Only strictly monotone rising or falling functions can be realised. This means x1 < x2.
--- [Input]
--- Input [value, object, storage]
--- X1 [value, object, storage]
--- Y1 [value, object, storage]
--- X2 [value, object, storage]
--- Y2 [value, object, storage]
--- [Output]
--- out - Output [object, storage]
function fbe_curve_2pt(input, x1, y1, x2, y2)
if input <= x1 then
return y1
elseif input >= x2 then
return y2
end
local n1, n2 = y2 - y1, x1 - x2
if n1 < 0 then
n1 = n1 * -1
n2 = n2 * -1
end
local c = n1 / n2
return y2 + (x2 - input) * c
end

--- [Function] fbe_curve_2pt_offset
--- Curve function with 2 points and offset
--- [Comment]
--- Depending on straight lines defined by 2 points, this module supplies an x-value for a y-value.
--- The first point of the straight line is defined by x1 and y1.
--- The second point of the straight line is defined by x2 and y2.
--- The x and the y-axis can be shifted by the respective offset.
--- If x is less than (x1 offset x), then y=y1.
--- If x is greater than (x2 offset x), then y=y2.
--- [Input]
--- Input [object, storage]
--- X1 [value, object, storage]
--- Y1 [value, object, storage]
--- X2 [value, object, storage]
--- Y2 [value, object, storage]
--- Offset X [value, object, storage]
--- Offset Y [value, object, storage]
--- [Output]
--- out - Output [object, storage]
function fbe_curve_2pt_offset(input, x1, y1, x2, y2, offsetX, offsetY)
if input <= (x1 + offsetX) then
return (y1 + offsetY)
elseif input >= (x2 + offsetX) then
return (y2+ offsetY)
end
local n1, n2 = y2 - y1, x1 - x2
if n1 < 0 then
n1 = n1 * -1
n2 = n2 * -1
end
local c = n1 / n2
return (y2 + offsetY) + ((x2 + offsetX) - input) * c
end
Reply
#6
Libraries from latest FB

Attached Files
.gz   Alerts.tar.gz (Size: 1.21 KB / Downloads: 13)
.gz   Comparator.tar.gz (Size: 1.93 KB / Downloads: 11)
.gz   Control.tar.gz (Size: 7.88 KB / Downloads: 12)
.gz   Converter.tar.gz (Size: 4.84 KB / Downloads: 9)
.gz   DALI.tar.gz (Size: 921 bytes / Downloads: 9)
.gz   Filter.tar.gz (Size: 743 bytes / Downloads: 7)
.gz   Gate.tar.gz (Size: 1.79 KB / Downloads: 7)
.gz   Math_advanced.tar.gz (Size: 4.3 KB / Downloads: 11)
.gz   Math_basic.tar.gz (Size: 1.83 KB / Downloads: 9)
.gz   Select_switch.tar.gz (Size: 1.66 KB / Downloads: 7)
.gz   String.tar.gz (Size: 2.95 KB / Downloads: 9)
.gz   Time.tar.gz (Size: 6.06 KB / Downloads: 10)
------------------------------
Ctrl+F5
Reply
#7
(14.01.2021, 10:46)Daniel. Wrote: Libraries from latest FB
I found the problem, without the offset the X is the input and the Y the output. In the one with offset the Y is the input and the X the output...

Reply
#8
The adapted script, where in both versions the X is input (outdoor air temperature for example) and the calculated Y is output.

--- [Function] fbe_curve_2pt
--- Curve function with 2 points
--- [Comment]
--- Depending on a straight line defined by 2 points, this module supplies a y-value for an x-value.
--- The first point of the straight line is defined by x1 and y1.
--- The second point of the straight line is defined by x2 and y2.
--- If x is less than x1, then y=y1.
--- If x is greater than x2, then y=y2.
--- Only strictly monotone rising or falling functions can be realised. This means x1 < x2.
--- [Input]
--- Input [value, object, storage]
--- X1 [value, object, storage]
--- Y1 [value, object, storage]
--- X2 [value, object, storage]
--- Y2 [value, object, storage]
--- [Output]
--- out - Output [object, storage]
function fbe_curve_2pt(input, x1, y1, x2, y2)
if input <= x1 then
return y1
elseif input >= x2 then
return y2
end
local n1, n2 = y2 - y1, x1 - x2
if n1 < 0 then
n1 = n1 * -1
n2 = n2 * -1
end
local c = -n1 * x1 - n2 * y1
return (-n1 * input - c) / n2
end

--- [Function] fbe_curve_2pt_offset
--- Curve function with 2 points and offset
--- [Comment]
--- Depending on straight lines defined by 2 points, this module supplies an x-value for a y-value.
--- The first point of the straight line is defined by x1 and y1.
--- The second point of the straight line is defined by x2 and y2.
--- The x and the y-axis can be shifted by the respective offset.
--- If x is less than (x1 offset x), then y=y1.
--- If x is greater than (x2 offset x), then y=y2.
--- [Input]
--- Input [object, storage]
--- X1 [value, object, storage]
--- Y1 [value, object, storage]
--- X2 [value, object, storage]
--- Y2 [value, object, storage]
--- Offset X [value, object, storage]
--- Offset Y [value, object, storage]
--- [Output]
--- out - Output [object, storage]
function fbe_curve_2pt_offset(input, x1, y1, x2, y2, offsetX, offsetY)
if input <= (x1 + offsetX) then
return y1
elseif input >= (x2 + offsetX) then
return y2
end
local n1, n2 = y2 - y1, x1 - x2
if n1 < 0 then
n1 = n1 * -1
n2 = n2 * -1
end
local c = -n1 * (x1 + offsetX) - n2 * (y1 + offsetY)
return (-n1 * input - c) / n2
end