Posts: 411
Threads: 163
Joined: May 2020
Reputation:
0
Hello
I have a problem with Modbus and SIEMENS V20 Inverter, I have 6 inverters address from 1 to 6, it happens to me that if I have modbus errors, I can no longer even drive the other inverters, indeed those present start and stop by themselves, from what can it depend?
I mapped the registers of the inverters in virtual objects in order not to overload the BIS KNX.
I directly use the addresses from some scrips for the command, and display some parameters.
I need help
thanks a lot
Posts: 5856
Threads: 31
Joined: Aug 2017
Reputation:
266
What errors do you have?
------------------------------
Ctrl+F5
Posts: 5856
Threads: 31
Joined: Aug 2017
Reputation:
266
Do you have any errors in modbus?
------------------------------
Ctrl+F5
Posts: 5856
Threads: 31
Joined: Aug 2017
Reputation:
266
In LogicMachine, under modbus tab, there is button Error log. What errors do you have there.
------------------------------
Ctrl+F5
Posts: 5856
Threads: 31
Joined: Aug 2017
Reputation:
266
Which FW is this?
------------------------------
Ctrl+F5
Posts: 5856
Threads: 31
Joined: Aug 2017
Reputation:
266
Can we get remote access? Send via PM if yes.
------------------------------
Ctrl+F5
Posts: 22
Threads: 6
Joined: Aug 2020
Reputation:
0
17.01.2021, 19:19
(This post was last modified: 17.01.2021, 19:45 by Hugo.)
May it helps: I currently have 6 Modbus connections running (TCP/IP by CAT 7 the network switches accordenly). I Could solve the same problem by the pollinterval since only two device connections are necessary every 5 seconds. First one fails and after about 5 hours it will by even not more possible to loog into the LM. Some pollintervals i set to 300 seconds some to 10 .... Everything has been wonderful since then. It always faild by the conections with 6 and more linked objects per divice. So may is also a god idear to think about whitch parameters are really needed to set into a object often. Even to add an Device twice is possibel so a few datas can by checked and setet into an object every 5 secondes and the other datas on the same device can by checked just ever 500 seconds since they are just informations how anyway will not change that often....