This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus TCP Read Failed
#1
Hello Dears
I have a Siemens Logo PLC modbus act as Modbus Srever
and I have two clients LM and Enterprise server from Schneider electric

I got these errors in the LM error log:
read failed: Broken pipe
read failed: connection reset by peer

first is it possible to have two clients in modbus TCP, if yes how to accomplish it without errors?

regards,
Best Regards,
Reply
#2
It is possible to have many modbus clients but it is fully up to the modbus server to handle. Try enabling persistent mode. Reboot your PLC and see it this helps.
------------------------------
Ctrl+F5
Reply
#3
(10.06.2021, 09:08)Daniel. Wrote: It is possible to have many modbus clients but it is fully up to the modbus server to handle. Try enabling persistent mode. Reboot your PLC and see it this helps.

thank you Daniel for your reply
I was using the same port for the two clients, which makes the issue

regards,
Best Regards,
Reply


Forum Jump: