Posts: 54
Threads: 15
Joined: Feb 2021
Reputation:
0
Hi,
I'm preparing scada screen for my project. Total 130 visualition pages maybe i could add 10 more.
CPU I/O load rate is 3.79 4.00 3.83. Would it be a problem for user ?
Thanks
Posts: 4935
Threads: 28
Joined: Aug 2017
Reputation:
225
CPU I/O should be below 1, Ideally 0.7. Your device is overloaded and it will not work correctly.
------------------------------
Ctrl+F5
Posts: 8069
Threads: 43
Joined: Jun 2015
Reputation:
470
The number of plans does not matter that much. What matters is the number of active user connections, bus load and scripts. As Daniel said your system is overloaded. Might be a script loop or a KNX/IP loop.
Posts: 4935
Threads: 28
Joined: Aug 2017
Reputation:
225
Wait half an hour and tell us how it changed. How often do you run this script?
------------------------------
Ctrl+F5
Posts: 54
Threads: 15
Joined: Feb 2021
Reputation:
0
CPU I/O level is now 0.7.And the Script running constanly.
Posts: 4935
Threads: 28
Joined: Aug 2017
Reputation:
225
What is the timer set to?
------------------------------
Ctrl+F5
Posts: 4935
Threads: 28
Joined: Aug 2017
Reputation:
225
This is way too fast. Temperature isn't changing fast anyway. You can set it to a minute easily.
------------------------------
Ctrl+F5
Posts: 54
Threads: 15
Joined: Feb 2021
Reputation:
0
Thanks a lot.Solved my issue.