This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

BACnet / export object list
#1
Hi
I have 2 questions.

We have a LM where we are exporting 1200 objects to BACnet, but sometimes some of them are not responding.
It is 600 1bit objects on/off and 600 1bit feedback objects.
Is this too much?

I could remove 50% of them and use the on/off as feedback.

Next question, is it possible to export the "objects" tab from LM? 

I need to give the CTS guys information on what state each object is and when it last changed.

Thanks in advance

Simon
Reply
#2
1. This should not be any problem for LM if all is configured correctly. What is the CPU/ID value? Is LM doing anything else?
2. Go to System-Network-BACnet objects.
------------------------------
Ctrl+F5
Reply
#3
(06.01.2025, 08:47)Daniel Wrote: 1. This should not be any problem for LM if all is configured correctly. What is the CPU/ID value? Is LM doing anything else?
2. Go to System-Network-BACnet objects.

CPU/IO: 0.02 0.01 0.00, Memory: 7%
There is no scripts or anything else running on the LM.

If I go to BACnet objects there is no timestamp of when the object have last changed value.
Reply
#4
What about KNX traffic?
https://forum.logicmachine.net/showthrea...9#pid37469
------------------------------
Ctrl+F5
Reply
#5
(06.01.2025, 09:11)Daniel Wrote: What about KNX traffic?
https://forum.logicmachine.net/showthrea...9#pid37469

TP is not connected on the LM. No push buttons no sensors everything is relays controlled through BACnet.
Reply
#6
Can you try using YABE and see if you have the same result?
------------------------------
Ctrl+F5
Reply
#7
I'm not on site atm, I can't use YEBA over ZEROTIER can I?

It worked perfectly with the LM Sync app, but 1 line is different the the others.

Code:
"updatetime":1732811320,"id":1103,"disablelog":1,"tagcache":"","address":1103,"datahex":"01","export":1,"comment":"","name":"Indvendig lys 2.0.X - 2.0.10 C4 DISP FB","datatype":1001
"securitykey":"","updatetime":1736124424,"id":1104,"disablelog":1,"tagcache":"","readoninit":0,"address":1104,"datahex":"01","units":"","pollinterval":"","export":1,"comment":"","name":"Indvendig lys 2.0.X - 2.0.11 C1 Blå - L1 T/S","datatype":1001
"updatetime":1736124426,"id":1105,"disablelog":1,"tagcache":"","address":1105,"datahex":"01","export":1,"comment":"","name":"Indvendig lys 2.0.X - 2.0.11 C1 Blå - L1 FB","datatype":1001
Why is that? They are configured exactly the same way.
Reply
#8
No this will not work over zerotier.
It is just knx security key(empty), hard to say without the backup.
------------------------------
Ctrl+F5
Reply
#9
When I download the file from LM Sync
My objects are in 3 states:

"datahex":"00"
"datahex":"01"
"datahex":""

Is this:

Off
On
"Have never been switched"
?
Reply
#10
00 = off, 01 = on, empty = value not set yet (defaults to off/0)
Reply