This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Additional registers for already mapped modbus
#1
Hi

Is there a smart way to add registers via a new/longer profile, than what the original profil was? 

I made a profile for a modbus component, thinking I was only going to monitor the device. Now I want to be able to write to a few more registers. 

Can i make a profile for the device with the new registers and add it to the same IP and the same modbus Address in the modbus list, without messing with the already funcioning mapping?

Thanks
Reply
#2
Yes you can.
------------------------------
Ctrl+F5
Reply
#3
Make sure that persistent connection mode is enabled for both devices. This way only a single connection will be used.
Reply
#4
One of my registers is reading "2". With this information, can I be sure the connection is established correct?
It's a R/W register, but when writing to it, it changes within a couple of seconds back to "2".

Is there anything I'm missing connection-wise, or is it the device that is refusing the change?

Thanks
Reply
#5
False alarm; I made the mistake of making my profile without incrementing the register no. by -1.

So once again thanks a lot to the "Read Test"!
Reply