05.02.2025, 09:41 
		
	
	
		Is it possible to make a backup of a LSS100100 and import it to a LM5Lp2 without any problems?
Best regards
Simon
	
	
	
Best regards
Simon
| 
					LSS100100 to LM5Lp2
				 | 
| 
		
		
		05.02.2025, 09:41 
		
	 
		Is it possible to make a backup of a LSS100100 and import it to a LM5Lp2 without any problems? Best regards Simon 
		
		
		05.02.2025, 09:45 
		
	 
		Yes but you need to make sure the firmware is equal or LM will have a newer version.  It might be confusing as we use different but you can share which firmware you have and we will advice. You cannot upload backup from newer firmware to older, other way around is fine.
	 
------------------------------ Ctrl+F5 
		Thank you LSS100100 is version 3.0.0 HW: Wiser for KNX (i.MX6) LM5Lp2 is version 20240426 LM5 Lite (i.MX6) 
		
		
		05.02.2025, 10:35 
		
	 
		Perfect, do I need to do the configuration or the project backup first?
	 
		
		
		05.02.2025, 11:16 
		
	 
		It's up to you. The System config is just system settings. You could probably set it manually. KNX settings are part of main backup.
	 
------------------------------ Ctrl+F5 
		
		
		05.02.2025, 11:26 
		
	 
		Got it. Last thing, Touch on the LSS100100 is that the same as Mosaic on LM5Lp2? If so can i just make a backup of that also and import it on LM5Lp2? 
		
		
		05.02.2025, 11:30 
		
	 
		No it's not 100% the same. To be honest I'm not sure, SE made many modification to Touch(it is based on Mosaic) . You can export just Touch (from Touch app) and import to Mosaic to see.  Anything cloud related on LSS100100 will not work on LM. We use our own cloud which is totally different to the SE. 
------------------------------ Ctrl+F5 | 
| 