Posts: 4
Threads: 2
Joined: Jan 2016
Reputation:
0
24.08.2017, 13:52
(This post was last modified: 24.08.2017, 13:54 by Demus.)
Hi!
I don't have any experience with Lm. But there is a device on the Modbus to link LM. Please help in creating a profile for the survey of inputs, outputs, and data registers. Map Delta DVP registers and Protocol description for them I've attached.
Thanks in advance for your help in the study of Lm.
Posts: 8972
Threads: 48
Joined: Jun 2015
Reputation:
510
Does it support Modbus RTU? Have you tried communicating with it using RTU read test? From the supplied documentation it seems that PLC uses Modbus ASCII which is not supported by the Modbus mapper.
Posts: 1820
Threads: 8
Joined: Jul 2015
Reputation:
121
24.08.2017, 21:43
(This post was last modified: 24.08.2017, 21:46 by Erwin van der Zwart.)
Hi,
Delta has there own protocol to a IP gateway, this gateway uploads data to the Delta Cloud Service and there is no API.
What i have done before is reading the Delta gateway's HTTP pages to get the data from it.
It's written for our HVAC SmartStruxure Lite controller, also LUA but it should be easy to port to the LM controller format.
Code: -- ******** Delta Solivia GW -> MPM module version 1.0 created by Erwin van der Zwart ******** 2015-12-10 ******** --
if not init then
-- Import libraries
require ("http")
-- Set timout for max wait time on HTTP response
http.TIMEOUT = 15
-- Delta Solivia GW Settings
IP_Address = '192.168.10.207'
UserName = 'admin'
PassWord = 'Schneider'
-- MPM objects
var("Absolute_Maximum_In_We_Object", "ME.AV44")
var("Percentage_Of_Nominal_Power_Object", "ME.AV45")
-- End init
init = true
else
-- Login before requesting data
if not login then
response = http.request('http://' .. IP_Address .. '/LoginCgi?ed_user=' .. UserName .. '&pw1=' .. PassWord .. '&logIn=Log+in')
-- Check if Response = successfully completed
for i in string.gmatch(response, '<body><br><h2 align="left"><font color="#339900">.-</font>') do
if i ~= nil then
responsestring = i:match([[color="#339900">(.-)</]])
--print(responsestring)
end
end
if responsestring == 'Operation successfully completed!' then
print('Login procedure ready, getting values..')
login = true
end
else
-- Get data from webservice
local data = http.request('http://' .. IP_Address .. '/Unbalanced.htm')
--print(data)
-- Check if data is received
if not data then
print('No data found.. , restarting procedure to try again..')
login = nil
return
end
-- Check if login is handled correct
for i in string.gmatch(data, '<h2>.-</h2>') do
if i ~= nil then
login_asked = i:match([[<h2>(.-)</h2>]])
if login_asked == 'Please log in' then
print('Login not ready or logged out, system will try to login again..')
login = nil
return
end
end
end
-- Power Balancing
for i in string.gmatch(data, '<input type="text".-</p>') do
if i ~= nil then
--print(i)
absolute_maximum_in_We = i:match([[name="t1" value="(.-)"]])
if absolute_maximum_in_We then
Absolute_Maximum_In_We_Object = absolute_maximum_in_We
print('Absolute maximum in We = ' .. absolute_maximum_in_We)
end
percentage_of_nominal_power = i:match([[name="t2" value="(.-)"]])
if percentage_of_nominal_power then
Percentage_Of_Nominal_Power_Object = percentage_of_nominal_power
print('Percentage of nominal power = ' .. percentage_of_nominal_power)
end
end
end
-- Add extra data pagefields here...
end --End Login
end -- End init
BR,
Erwin
Posts: 4
Threads: 2
Joined: Jan 2016
Reputation:
0
25.08.2017, 06:19
(This post was last modified: 25.08.2017, 06:26 by Demus.)
(24.08.2017, 17:42)admin Wrote: Does it support Modbus RTU? Have you tried communicating with it using RTU read test? From the supplied documentation it seems that PLC uses Modbus ASCII which is not supported by the Modbus mapper.
Yes, Modbus rtu is supported. He included me in the PLC. Test to read from register LM is successful. I have difficulties to describe the profile line to read for example the register D0 at the address 4096.
With this option the register is not read. Don't understand what the problem is.
{ "name": "Input 1", "bus_datatype": "float16", "type": "inputregister", "address": 4096, "value_multiplier": 0.001, "units": "V" },
{ "name": "Input 2", "bus_datatype": "float16", "type": "inputregister", "address": 4096, "value_multiplier": 0.001, "units": "V" },
(24.08.2017, 21:43)Erwin van der Zwart Wrote: Hi,
Delta has there own protocol to a IP gateway, this gateway uploads data to the Delta Cloud Service and there is no API.
What i have done before is reading the Delta gateway's HTTP pages to get the data from it.
It's written for our HVAC SmartStruxure Lite controller, also LUA but it should be easy to port to the LM controller format.
Code: -- ******** Delta Solivia GW -> MPM module version 1.0 created by Erwin van der Zwart ******** 2015-12-10 ******** --
if not init then
-- Import libraries
require ("http")
-- Set timout for max wait time on HTTP response
http.TIMEOUT = 15
-- Delta Solivia GW Settings
IP_Address = '192.168.10.207'
UserName = 'admin'
PassWord = 'Schneider'
-- MPM objects
var("Absolute_Maximum_In_We_Object", "ME.AV44")
var("Percentage_Of_Nominal_Power_Object", "ME.AV45")
-- End init
init = true
else
-- Login before requesting data
if not login then
response = http.request('http://' .. IP_Address .. '/LoginCgi?ed_user=' .. UserName .. '&pw1=' .. PassWord .. '&logIn=Log+in')
-- Check if Response = successfully completed
for i in string.gmatch(response, '<body><br><h2 align="left"><font color="#339900">.-</font>') do
if i ~= nil then
responsestring = i:match([[color="#339900">(.-)</]])
--print(responsestring)
end
end
if responsestring == 'Operation successfully completed!' then
print('Login procedure ready, getting values..')
login = true
end
else
-- Get data from webservice
local data = http.request('http://' .. IP_Address .. '/Unbalanced.htm')
--print(data)
-- Check if data is received
if not data then
print('No data found.. , restarting procedure to try again..')
login = nil
return
end
-- Check if login is handled correct
for i in string.gmatch(data, '<h2>.-</h2>') do
if i ~= nil then
login_asked = i:match([[<h2>(.-)</h2>]])
if login_asked == 'Please log in' then
print('Login not ready or logged out, system will try to login again..')
login = nil
return
end
end
end
-- Power Balancing
for i in string.gmatch(data, '<input type="text".-</p>') do
if i ~= nil then
--print(i)
absolute_maximum_in_We = i:match([[name="t1" value="(.-)"]])
if absolute_maximum_in_We then
Absolute_Maximum_In_We_Object = absolute_maximum_in_We
print('Absolute maximum in We = ' .. absolute_maximum_in_We)
end
percentage_of_nominal_power = i:match([[name="t2" value="(.-)"]])
if percentage_of_nominal_power then
Percentage_Of_Nominal_Power_Object = percentage_of_nominal_power
print('Percentage of nominal power = ' .. percentage_of_nominal_power)
end
end
end
-- Add extra data pagefields here...
end --End Login
end -- End init
BR,
Erwin
I think you are on the other controllers speak. I'm working with this on rs-485.
http://www.deltaww.com/Products/Category...2%20Series
Posts: 8972
Threads: 48
Joined: Jun 2015
Reputation:
510
Try changing type to "register"
Posts: 4
Threads: 2
Joined: Jan 2016
Reputation:
0
25.08.2017, 06:56
(This post was last modified: 25.08.2017, 07:07 by Demus.)
(25.08.2017, 06:49)admin Wrote: Try changing type to "register"
Thank you very much! Works!
One more question. Can I one and the same port to use for the survey using a script and using the profile? Devices are polled different.
Posts: 8972
Threads: 48
Joined: Jun 2015
Reputation:
510
Yes, but modbus proxy functions must be used, see this post for more info: https://forum.logicmachine.net/showthrea...53#pid1953
|