Posts: 92
Threads: 31
Joined: Feb 2016
Reputation:
0
Hi, I have a question about a iem3155 Energy Meter and LM5, I need to make a trend with a kwh in a hour period and the meter only give me a total kwh that it read, I try to make a script that subtract the two values readed in one hour period, Can you help me to make this script? Exist another possibility yo make this? Thank you very much!
Posts: 1764
Threads: 6
Joined: Jul 2015
Reputation:
117
20.12.2017, 19:31
(This post was last modified: 20.12.2017, 19:31 by Erwin van der Zwart.)
Hi,
Create a trend with type "counter" for this and set the trend resolution to 1 hour..
BR,
Erwin
Posts: 1764
Threads: 6
Joined: Jul 2015
Reputation:
117
Hi,
That’s exactly what a counter trend does, just try one then you see what i mean.
It only shows the (calculated) power used (difference) in every hour.
You can extract this hour usage data with trend.fetch when you want to report something.
BR,
Erwin
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
12.01.2018, 16:58
(This post was last modified: 12.01.2018, 19:33 by Mr.D.)
Hi,
Is there a way to have the trend resolution larger than 1 hour, like 24 hours or even weekly/monthly?
BR
Mr.D
Posts: 4643
Threads: 24
Joined: Aug 2017
Reputation:
207
(12.01.2018, 16:58)Mr. Danielsen Wrote: Hi,
Is there a way to have the trend resolution larger than 1 hour, like 24 hours or even weekly/monthly?
BR
Mr.D
Just look on the Trend app and you will see it on right side. All this is there out of the box.
BR
------------------------------
Ctrl+F5