19.03.2019, 12:35
Hello!
Is it possible to setup a Homelynk as a Modbus slave on TCP/IP?
Regards!
P
Regards!
P
HomeLynk as Modbus TCP/IP slave
19.03.2019, 12:35
Hello!
Is it possible to setup a Homelynk as a Modbus slave on TCP/IP? Regards! P
19.03.2019, 12:36
20.03.2019, 07:09
Thanks!
/P
29.03.2019, 09:26
Hello!
This works fine in genneral but I have an issue with the temperature. When I set the datatype in the script to float16 I get wrong scale on the modbus side. For example if the temperature value is 7.5 on KNX side I get value 7 on modbus side. I should get 750. If I change the datatype in script to int16 it gets completely wrong because temperature on KNX are float16. Are there any way to integrate a multiplier in the script only for float16 objects?
29.03.2019, 10:00
You should make the conversion outside the script. Use an virtual object for modbus and make simple event script like this.
Code: grp.update('virtual object address', event.getvalue()*100)
08.11.2019, 07:00
Hello!
Are there any limitations of the amount of adresses in this script above? Or are there any ather better way if there is a lot of adresses? I have a project where I have a modbus master that have to read about 300 adresses. BR Per-Åke
08.11.2019, 07:59
(This post was last modified: 08.11.2019, 08:00 by Erwin van der Zwart.)
Hard to say exactly as it depends on other processes in your controller like amount of KNX object updates etcetera. The indicator of limitations is most of the time the CPU load. We tested a lot of scenarios / addressable limits and you can see them in this document: https://www.schneider-electric.com/en/download/document/AN017/ On page 13 you can see the results of a test with 1000 objects on a HW2 device (you can increase this on HW3). So if your controller is not doing anything else then 300 objects should work just fine. BR, Erwin
17.09.2020, 08:32
I have a problem with the script..
I have 2 LM: LM1 is the one with this script https://openrb.com/lm-as-modbus-tcp-slave LM2 is the one that need to read LM1 When I try to read with LM1 my LM2, LM2 return tis error: LM (TCP 192.168.1.91:502) read failed: Illegal data address The profile in LM2 is this: Code: {
"manufacturer":"LM",
"description":"LM",
"mapping":[
{"name":"Reg1", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 0, "writable": true},
{"name":"Reg2", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 1, "writable": true},
{"name":"Reg3", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 2, "writable": true},
{"name":"Reg4", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 3, "writable": true},
{"name":"Reg5", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 4, "writable": true},
{"name":"Reg6", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 5, "writable": true},
{"name":"Reg7", "bus_datatype": "int16", "datatype": "uint16", "type": "register", "address": 6, "writable": true}
}Code: if not mb then
require('luamodbus')
-- Elenco mappature bobine, a partire da 0
coils = { '1/1/1' }
-- Elenco mappature dei registri, a partire da 0
registers = { "1/2/0", "1/2/3", "1/2/4", "1/2/9", "1/2/14", "1/2/16", "33/0/1" }
-- Elenco tipo di dati del registro, il conteggio degli elementi deve corrispondere alla tabela dei registri
regdt = { dt.uint16, dt.uint16, dt.uint16, dt.uint16, dt.uint16, dt.uint16, dt.uint16 }
-- Richiamo in scrittura del gr. KNX
function knxgroupwrite(event)
local value
-- Prova a trovare la bobona corrispondente
for id, addr in ipairs(coils) do
if event.dst == addr then
value = knxdatatype.decode(event.datahex, dt.bool)
mb:setcoils(id - 1, value)
-- Prova a trovare il registro corrispondente
for id, addr in ipairs(registers) do
value = knxdatatype.decode(event.datahex, regdt[ id ])
mb:setregisters(id - 1, value)
-- richiama bobina in scrittura
function mbwritecoils(coil, value)
local addr = coils[ coil + 1 ]
if addr then
grp.write(addr, value, dt.bool)
-- registra la chiamata in scrittura
function mbwriteregisters(register, value)
local addr = registers[ register + 1 ]
if addr then
grp.write(addr, value, regdt[ register + 1])
-- knx group monitor, gestisce le scritture di gruppo
knxclient = eibdgm:new({ timeout = 0.1 })
knxclient:sethandler('groupwrite', knxgroupwrite)
-- modbus slave, ascolta su tutte le interfaccie e porte default 502
mb = luamodbus.tcp()
mb:open('0.0.0.0', 502)
-- Impostazione Slave (Facoltativa)
--mb:setslave(1)
mb:setreceivetimeout(0.1)
mb:setmapping(#coils, 0, #registers, 0)
-- Inizializza bobine
value = grp.getvalue(addr)
-- Inizializza registri
-- set callbacks for coil and register write
mb:setwritecoilcb(mbwritecoils)
mb:setwriteregistercb(mbwriteregisters)
-- Gestione modbus e KNX
mb:handleslave()
knxclient:step()
17.09.2020, 08:37
Why do you need modbus to communicate between two LMs?
It is only a test, I need to read from an LM with modbus TCP
17.09.2020, 09:52
I just tried it like this and it works fine.
coils = { '32/1/23' }
registers = { "32/1/21", "32/1/22" }
regdt = { dt.uint16, dt.uint16 }
local value
if addr then
if addr then
--mb:setslave(1)
mb:handleslave()
knxclient:step()Code: {
"manufacturer": "Embedded Systems",
"description": "LM11",
"mapping": [
{ "name": "Output 1", "bus_datatype": 1, "type": "coil", "address": 0, "writable": 1 },
{ "name": "Input 1", "bus_datatype": 7, "type": "register", "address": 0, "writable": 1 },
{ "name": "Input 1", "bus_datatype": 7, "type": "register", "address": 1, "writable": 1 }
17.09.2020, 09:57
what!?
how is it possible? ![]() Can I know how you set objects?
mmm really strange.. now that I use the same datatype (my fault) I have no error, but I read always 0, no matter what I write into objects..
The FW is 20200116
17.09.2020, 10:13
Do you use same type objects in both LMs? It works fine in both directions.
Disable and enable the script.
Ctrl+F5 |