Hello,
I am using LM5 Lite with KNX system and there are Hager TYA670D DALI gateways to control DALI luminaires. The gateway can give 1byte and 2byte error status. I want to show individual failure message for per DALI load on the visualization page.
- How can I use these error status messages?
- Is there any visualization template about this?
Thanks and regards,
İbrahim.
Posts: 5874
Threads: 35
Joined: Aug 2017
Reputation:
269
You need to decode them and write result to individual new objects.
------------------------------
Ctrl+F5
Posts: 8972
Threads: 48
Joined: Jun 2015
Reputation:
510
1-byte status (238.600 data type) is supported in the latest firmware so no need to decode manually.
Posts: 43
Threads: 8
Joined: Mar 2020
Reputation:
0
Hello,
Thanks for reply.
-If there is more than 1 device has failure in the same DALI line, the status is changing cyclical in 64 seconds. How can I store decoded message for per DALI address? or should I just show a text message about which address has a failure?
-For the visualization, can I use three information for status? For example, image-1 for on, image-2 for off and image-3 for failure.
Regards,
İbrahim.
Posts: 5874
Threads: 35
Joined: Aug 2017
Reputation:
269
Hi
Out of the box you can show the text. If you want to make individual then it will require manual decoding and object per light where you will write the state.
Out of the box this object display OK state for off icon and error for ON icon, there is no third state. Again if you want you can make a script where you can check the light status and the failure and write this to a byte object in which you can define different icons depend of the value.
BR
------------------------------