Hi everyone,
I've integrated a Caleffi Conteca device on my LM and everything works well. I'll share my .json just after I'll solve this problem.
I would like to add the register in attached and have a different GA output for every kind of alarm. For example:
- bit0 - Errore on Flow Temperature - 0/5/0
- bit1 - Errore on return temperature - 0/5/1
- bit6 - Low Battery Alarm - 0/5/2
and go on for the other bit of alarm.
Can someone explain me how to do?
Thanks in advance.
Attached Files
Thumbnail(s)
Posts: 4663
Threads: 24
Joined: Aug 2017
Reputation:
213
------------------------------
Ctrl+F5
Posts: 13
Threads: 4
Joined: Jan 2024
Reputation:
2
(04.10.2024, 15:59) Daniel Wrote: see this
https://forum.logicmachine.net/showthrea...29#pid6729
Hi Admin and thanks for your answer.
My LogicMachine knowledge is not so pro to let me know how go on with this issue. Can you halp me a little bit more?
Code:
{
"name": "Alarm Status - bit 0 - Error flow temperature",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask" : what can I use for reading bit0?
"value_custom": {"01": "OK", "1": "Alarm"}
},
{
"name": "Alarm Status - bit 1 - Error return temperature",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask" : what can I use for reading bit1?
"value_custom": {"01": "OK", "1": "Alarm"}
},
Please consider to help me.
Posts: 7782
Threads: 42
Joined: Jun 2015
Reputation:
448
Use this. I've also fixed incorrect value_custom (should be "0" instead of "01").
Code:
{
"name": "Alarm Status - bit 0 - Error flow temperature",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x01,
"value_custom": {"0": "OK", "1": "Alarm"}
},
{
"name": "Alarm Status - bit 1 - Error return temperature",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x02,
"value_custom": {"0": "OK", "1": "Alarm"}
},
Posts: 13
Threads: 4
Joined: Jan 2024
Reputation:
2
07.10.2024, 08:34
(This post was last modified: 07.10.2024, 08:35 by Tuwat47 .)
Hi Admin I don't have my LM for testing the result, but what do you think if I use this kind of .json for reading every single bit?
Code:
{
[
{
"name": "Alarm - bit 0 - Error flow temperature",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x1,
"value_custom": {"01": "OK", "1": "Alarm"}
},
{
"name": "Alarm - bit 1 - Error return temperature",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x2,
"value_custom": {"01": "OK", "1": "Alarm"}
},
{
"name": "Alarm - bit 6 - Low battery alarm",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x40,
"value_custom": {"01": "OK", "1": "Alarm"}
},
{
"name": "Alarm - bit 8 - Measurament unit mismatch on main counter",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x100,
"value_custom": {"01": "OK", "1": "Alarm"}
},
{
"name": "Alarm - bit 9 - Measurament unit mismatch on counter 1",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x200,
"value_custom": {"01": "OK", "1": "Alarm"}
},
{
"name": "Alarm - bit 10 - Measurament unit mismatch on counter 2",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x400,
"value_custom": {"01": "OK", "1": "Alarm"}
},
{
"name": "Alarm - bit 11 - Measurament unit mismatch on counter 3",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x800,
"value_custom": {"01": "OK", "1": "Alarm"}
},
{
"name": "Alarm - bit 12 - Measurament unit mismatch on counter 4",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x1000,
"value_custom": {"01": "OK", "1": "Alarm"}
},
]
}
If it will work I'll post my .json for Caleffi Conteca.
(07.10.2024, 08:20) admin Wrote: Use this. I've also fixed incorrect value_custom (should be "0" instead of "01").
Code:
{
"name": "Alarm Status - bit 0 - Error flow temperature",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x01,
"value_custom": {"0": "OK", "1": "Alarm"}
},
{
"name": "Alarm Status - bit 1 - Error return temperature",
"bus_datatype": "bool",
"datatype": "uint16",
"type": "register",
"address": 119,
"value_bitmask": 0x02,
"value_custom": {"0": "OK", "1": "Alarm"}
},
Ok, perfect. I will try as soon as possible. Thanks in advance for your help Admin.
Posts: 7782
Threads: 42
Joined: Jun 2015
Reputation:
448
Fixed profile attached.