This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

BACnet PICS
#1
Hi.
Where can I find the BACnet PICS for the LogicMachine4?
Does the LM4 support BACnet COV, Schedule, Trend, Alarm and Event, etc?
-Espen-
Reply
#2
LM conforms to BACnet Application Specific Controller (B-ASC) profile. COV is supported; Schedule, Trend, Alarm and Event are not.

Attached Files Thumbnail(s)
   
Reply
#3
(03.11.2015, 11:51)admin Wrote: LM conforms to BACnet Application Specific Controller (B-ASC) profile. COV is supported; Schedule, Trend, Alarm and Event are not.

How can I setup the COV's for the LM4? Are these determined by the BACnet-client (reading of the BACnet-objects)?
-espen-
Reply
#4
You don't have to configure anything, remote devices subscribe to object COV notifications. There can be 32 active subscriptions.
COV has default delta of 1, for now it can only be changed from BACnet side by other devices. Keep in mind that BACnet service restart or full LM restart will reset COV delta to 1.
Reply