This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus TCP/IP: value send behaviour
#1
Hi there,
I use a LM as master modbus via TCP/IP.

When the slave (ONLY THE SLAVE) goes off, what happen when power goes back? 

Does the LM send its value to the slave again?

Thank you for your help.

BR
Reply
#2
(22.10.2021, 14:11)Domoticatorino Wrote: Hi there,
I use a LM as master modbus via TCP/IP.

When the slave (ONLY THE SLAVE) goes off, what happen when power goes back? 

Does the LM send its value to the slave again?

Thank you for your help.

BR
Try to create a script with the object connection status
Reply
#3
The values are not sent again automatically. Using an event script mapped to the device status object might work but only if the objects are write-only. Otherwise the current Modbus register values will overwrite previous values before the script runs.