Posts: 54
Threads: 15
Joined: Feb 2021
Reputation:
0
Hi,
I'm preparing scada screen for my project. Total 130 visualition pages maybe i could add 10 more.
CPU I/O load rate is 3.79 4.00 3.83. Would it be a problem for user ?
Thanks
Posts: 5817
Threads: 31
Joined: Aug 2017
Reputation:
266
CPU I/O should be below 1, Ideally 0.7. Your device is overloaded and it will not work correctly.
------------------------------
Ctrl+F5
Posts: 8931
Threads: 48
Joined: Jun 2015
Reputation:
508
The number of plans does not matter that much. What matters is the number of active user connections, bus load and scripts. As Daniel said your system is overloaded. Might be a script loop or a KNX/IP loop.
Posts: 5817
Threads: 31
Joined: Aug 2017
Reputation:
266
Wait half an hour and tell us how it changed. How often do you run this script?
------------------------------
Ctrl+F5
Posts: 54
Threads: 15
Joined: Feb 2021
Reputation:
0
CPU I/O level is now 0.7.And the Script running constanly.
Posts: 5817
Threads: 31
Joined: Aug 2017
Reputation:
266
What is the timer set to?
------------------------------
Ctrl+F5
Posts: 5817
Threads: 31
Joined: Aug 2017
Reputation:
266
This is way too fast. Temperature isn't changing fast anyway. You can set it to a minute easily.
------------------------------
Ctrl+F5
Posts: 54
Threads: 15
Joined: Feb 2021
Reputation:
0
Thanks a lot.Solved my issue.