This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LM bacnet
#1
Hi,I used two LMs for bacnet application testing, one for the client and the other for the server,

I installed the ". ipk" file on the attachment on the client's LM. I successfully found the server LM, but I could not find any data points on the server. It can be determined that I have selected the 'Server enabled' function for the bacnet server LM, and I have selected the 'Export' function for the knx group objects in the LM.

Can someone help me? Huh Thank you in advance.

Attached, I also uploaded a screenshot of the LM bacnet client.

Attached Files Thumbnail(s)
   
.ipk   bacnet-client.ipk (Size: 2.24 MB / Downloads: 11)
Reply
#2
Are you doing it on same LM?
------------------------------
Ctrl+F5
Reply
#3
No, two gateways are used, one as the bacnet client and the other as the server. The image in post 1 is the client LM.
Reply
#4
Use Yabe on PC to see if your server works.
------------------------------
Ctrl+F5
Reply
#5
(24.03.2023, 09:40)Daniel Wrote: Use Yabe on PC to see if your server works.

I installed this package named 'genohm-scada-bacnet_20230120'(through System Config > System > Packages > Add (+)) on the client LM
package:
https://dl.openrb.com/lm-23-imx6/pkg/gen...0_imx6.ipk
https://dl.openrb.com/lm-23-imx6/pkg/gen...0_imx6.sig

I successfully searched the server device and all data points on the client LM through LogicMachine > bacnet > scan network.Therefore, it is ruled out that the server does not work.So I think it's the problem in post #1:bacnet-client.ipk
Reply
#6
There are two implementations of bacnet client. App or script. The packages you installed are for script.
https://openrb.com/logicmachine-as-bacnet-client/
------------------------------
Ctrl+F5
Reply
#7
Yes, I know that there are two client configuration methods. The script method allows me to search the service device's alldata points normally, but not through the APP method. The APP of client needs to be further improved.
Reply
#8
This is 3rd party app not done by us.
------------------------------
Ctrl+F5
Reply
#9
APP can directly map bacnet data points through kxn group addresses, which is particularly convenient. I hope it can be improved.

If there are many data points in the script method, I use the resident script to read all the data, which can be slow to read, resulting in an unsatisfactory overall control effect.
Reply
#10
App is slower than scripts.
From a script all device objects can be read with a single call which can be faster than polling each value separately. See this: https://forum.logicmachine.net/showthrea...7#pid22457
Reply
#11
Thank you for your answer. I will communicate with you further after the test: