This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus: permanent connection???
#1
I have a question about the modbus-connection (TCP) in LM.

When I add a new device (see screenshot), I can select: permanent connection. (Forgive me if the translation is not 100% correct, but I have a dutch version). What does it do?

I have looked in the manual, but I didn't really find an answer to my question.

When I check the option, the CPU of the LM goes sometimes in red. But, when I uncheck it, the CPU sty's blue. So, I wondering what is the real cause of it, and if there is something else wrong.

Attached Files Thumbnail(s)
   
Reply
#2
Some TCP devices have limited amount of connections and they go offline after a while. Whit persistent mode the connection is never closed. Normally this is not needed, only on some devices.
------------------------------
Ctrl+F5
Reply