This forum uses cookies
This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus bug
#1
I've found that when I've change ga which is connected to coil and coil should be updated then its not updated to show its current value.

E.g.
I have writable coil for vacuum-cleaner mode status in recuperator. When I try to switch-off it from modbus while relay switch is closed then LM in mapper shows updated status(is off) but I know that this is not true and also when I try read coil value by LM Read test then it returns that vacuum-cleaner mode is on.
Done is better than perfect
Reply
#2
Post your device profile.
Reply
#3
(03.12.2018, 13:30)admin Wrote: Post your device profile.

Profile attached. This coil was not set as writable(I've updated it now, attached not updated version). Now I probably understand how it works, when it is not writable modbus mapper compare modbus value with knx ga only on init and then only when modbus value change. All ga change is ignored so when ga value change it won't be updated to real value from modbus until modbus value will change.

Attached Files
.json   Enervent_Goscinna_desc.json (Size: 22.49 KB / Downloads: 2)
Done is better than perfect
Reply