I need some help with theese values
{ "name": "Device Firmware build", "bus_datatype": "int16", "type": "inputregister", "address": 6003, "writable": 0, "units": " " },
{ "name": "Temperature Controller method", "bus_datatype": "bool", "type": "register", "address": 5130, "writable": 1, "units": " " },
{ "name": "Temperature setpoint", "datatype": "int16", "bus_datatype": "float16", "type": "register", "address": 5101, "writable": 1, "units": "C", "value_multiplier": 0.1 },
{ "name": "Travelling mode temperature drop", "datatype": "int16", "bus_datatype": "float16", "type": "register", "address": 5107, "writable": 1, "units": "C", "value_multiplier": 0.1 },
{ "name": "Away State Temperature Drop", "datatype": "int16", "bus_datatype": "float16", "type": "register", "address": 5171, "writable": 1, "units": "C", "value_multiplier": 0.1 },
{ "name": "OperatingModeStatus", "bus_datatype": "int16", "datatype": "int16", "type": "inputregister", "address": 6302, "writable": 0},
3x6003
R
Device Firmware build
0
999
4x5130
RW
Temperature Controller method
0-1
0 = Supply air, 1 = Room air
4x5101
RW
Temperature setpoint
16-23°C
Supply/Room temperature controller setpoint
4x5107
RW
Travelling mode temperature drop
0-10°C
Temperature drop of Setpoint
4x5171
RW
Away State Temperature Drop
0-10°C
Temperature drop of Setpoint
3x6302
R
Ventilation Speed state
0-4
0 = Stopped, 1= Away, 2 = Home, 3 = Boost
{ "name": "Device Firmware build", "bus_datatype": "int16", "type": "inputregister", "address": 6003, "writable": 0, "units": " " },
{ "name": "Temperature Controller method", "bus_datatype": "bool", "type": "register", "address": 5130, "writable": 1, "units": " " },
{ "name": "Temperature setpoint", "datatype": "int16", "bus_datatype": "float16", "type": "register", "address": 5101, "writable": 1, "units": "C", "value_multiplier": 0.1 },
{ "name": "Travelling mode temperature drop", "datatype": "int16", "bus_datatype": "float16", "type": "register", "address": 5107, "writable": 1, "units": "C", "value_multiplier": 0.1 },
{ "name": "Away State Temperature Drop", "datatype": "int16", "bus_datatype": "float16", "type": "register", "address": 5171, "writable": 1, "units": "C", "value_multiplier": 0.1 },
{ "name": "OperatingModeStatus", "bus_datatype": "int16", "datatype": "int16", "type": "inputregister", "address": 6302, "writable": 0},
3x6003
R
Device Firmware build
0
999
4x5130
RW
Temperature Controller method
0-1
0 = Supply air, 1 = Room air
4x5101
RW
Temperature setpoint
16-23°C
Supply/Room temperature controller setpoint
4x5107
RW
Travelling mode temperature drop
0-10°C
Temperature drop of Setpoint
4x5171
RW
Away State Temperature Drop
0-10°C
Temperature drop of Setpoint
3x6302
R
Ventilation Speed state
0-4
0 = Stopped, 1= Away, 2 = Home, 3 = Boost