This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus, getting bits in a register
#1
Hi,
How can I read out single bits from a 16-bit register? And write the bit to a group address? The modbus addresses in the readcoils function are not the same as for the readinputs addresses.
I also want a tip how I can read signed 16-bit register? (out side air temperature)

Espen Big Grin
Reply
#2
Hi,


If you read a 16 bits integer register you can get back value 0 to 65535, but when this register is used as single bit (not coil) you probably get back only value 0 or 1 out of this register.

To use that value for a 1 bit KNX value you can simply transfer it to boolean by using this:

Code:
12345
value = mb:readregisters(123) if value == 0 or value == 1 then  value = toboolean(value)  grp.write('1/1/1', value) end
To set 16 bits register value to 2 byte signed you can use this code:
Code:
123
r1 = mb:readregisters(124) value = lmcore.inttohex(r1, 2) value = knxdatatype.decode(value, dt.int16)

BR,
Erwin
Reply
#3
If your register is not a bitmask but a single bit you can write it directly to a boolean object, any numeric value other than 0 will be treated as true. As for reading int16, you can use this:
Code:
1
value = mb:readregistervalue(123, 'int16')
Reply
#4
My 16-bit register is a bitmask, e.g.:
Input register 3x0006 consists of:
Bit 0 = Dampers open
Bit 1 = Fire dampers open
Bit 2 = Fire dampers closed
Bit 3 = Status feedback pump
Etc.

I'm interested in getting out the status of a single bit within a register. Not the whole register acting as a bit, 0 or 1.
Is it possible?
Reply
#5
You can use this helper function:
Code:
1234567891011
function getbit(value, nr)   value = bit.rshift(value, nr)   return bit.band(value, 1) end value = mb:readregisters(123) if value then   dampers_open = getbit(value, 0)   fire_dampers_open = getbit(value, 1)   ... end
Reply
#6
Thanks!
Reply
#7
(22.12.2016, 10:47)admin Wrote: You can use this helper function:
Code:
1234567891011
function getbit(value, nr)   value = bit.rshift(value, nr)   return bit.band(value, 1) end value = mb:readregisters(123) if value then   dampers_open = getbit(value, 0)   fire_dampers_open = getbit(value, 1)   ... end

Its work for read any bit of 16bit register.

i also write any bit of 16bit register this like..

Code:
12345
function updatebit(bit_value, ModbusAddress, bit_no)   ????   ????   ???? end



For example;

Code:
12
 updatebit (true, 123, 0)  updatebit (false, 123, 5)
1. --
before modbus 123 register: 1010 1101 0110 1011 (=44.395)
after modbus 123 register: 1010 1101 0110 1010 (=44.394)
2.--
before modbus 123 register: 1010 1101 0110 1010 (=44.394)
after modbus 123 register: 1010 1101 0100 1010 (=44.362)
Reply