This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Statistics
#1
Hi! 
In LogicMachine-Objects (tab) I have these values
   

and these statistics
   

I don’t understand why I have more TP repeats than TP loads. Is it worrying?

Are them normal? I think it is no normal, but I don't know how to solve it.

thanks
Reply
#2
The usual cause are LM group addresses that are not linked to any KNX devices on the TP bus.

You should either use virtual group addresses or disable "write to bus" option where applicable. In scripts use grp.update/grp.checkupdate for such group addresses.

In general your system looks very healthy.
------------------------------
Ctrl+F5
Reply
#3
Hi! thanks for your asnwer. 
During the day with more activity in the buildings, these are the results.
   

and statistics
   

"In general your system looks very healthy." I thought that I need to improve it.

The cause of Repeats, maybe is because I have the sniffer active?
   

I made that I have unknown object in Logic Machine.
   

PD: as you see, the background is yellow. some objects are green.
What is the meaning of the colours?
Thanks.
Reply
#4
Green is when a object receives new telegram, yellow is when object has no name and it was sniffed from the bus. When importing KNX project select: Update existing objects:
If you have another KNX device which is spamming the bus then you can select: ACK all group telegrams in KNX connection settings but it is better to investigate who does it. This will work only for telegrams which are not sent by LM, for telegrams which are sent by LM see my earlier comment.
------------------------------
Ctrl+F5
Reply
#5
thanks, this phrase " You should either use virtual group addresses or disable "write to bus" option where applicable. In scripts use grp.update/grp.checkupdate for such group addresses."

where is "write to bus"? is a group address option in ETS?
Reply
#6
This option you will find when integrating other protocols to LM like modbus/zigbee or in Visu itself.
Nothing to do with ETS.
------------------------------
Ctrl+F5
Reply