Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
Hi,
I am getting the following error in my error log:
Schneider (RTU slave 1) read failed: Operation timed out
Schneider (RTU slave 1) read failed: Response not from requested slave
Scriptname is modbus, but I have no script called modbus.
The error happens several times each hour. At different times during each our...
BR,
Mr.D
Posts: 7764
Threads: 42
Joined: Jun 2015
Reputation:
447
This is coming from Modbus mapper, try increasing timeout value for your devices.
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
Hi,
Ok, I'll give that a try.
Just so I understand, what does the time out value do?
It is no set as default 0.5 I think...?
BR
Mr.D
Posts: 4646
Threads: 24
Joined: Aug 2017
Reputation:
207
(25.01.2018, 08:06)Mr. Danielsen Wrote: Hi,
Ok, I'll give that a try.
Just so I understand, what does the time out value do?
It is no set as default 0.5 I think...?
BR
Mr.D
It waits that long for answer from slave. If answer not received in this time then error: Operation timed out
------------------------------
Ctrl+F5
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
Hi,
I have altered the time out value to 15, but I am still getting the same errors...
Any other suggestions?
BR,
Mr.D
Posts: 4646
Threads: 24
Joined: Aug 2017
Reputation:
207
(25.01.2018, 16:49)Mr. Danielsen Wrote: Hi,
I have altered the time out value to 15, but I am still getting the same errors...
Any other suggestions?
BR,
Mr.D
Check your wiring. Make sure gnd is connected.
------------------------------
Ctrl+F5
Posts: 1764
Threads: 6
Joined: Jul 2015
Reputation:
117
Hi,
How many devices are connected? Can it be that you have a duplicate slave address?
How long is your cabling? Do you have EOL termination?
BR,
Erwin
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
25.01.2018, 19:51
(This post was last modified: 25.01.2018, 19:54 by Mr.D.)
Hi,
Gnd is connected... I have tried with and without, still the same errors.
I only have a iEM 3150 Schneider connected as slave 1. This is the only device connected.
EOL Termination? I have no idea because I do not know what that is.
The cable I have used is a Cat5 network cable and it is about 1 meter long.
My pull interval is 10 seconds, time out value is 5
BR,
Mr.D
Edit:
I have now tried to change slave/device settings from slave 1 to 2... and still same error...
Posts: 1764
Threads: 6
Joined: Jul 2015
Reputation:
117
25.01.2018, 22:50
(This post was last modified: 25.01.2018, 22:55 by Erwin van der Zwart.)
Hi,
EOL termination means placing a resistor parallel over the "end of line", this is required by the Modbus standard to avoid reflections but when using just a 1m cable i don't think it will make a difference.
Are you sure the RS485 port is not called from another process? (like from modbus template and also from script), did you try to restart the controller to be sure there is no old script still loaded?
If that is not the case then i would suggest to test with a new cable between the meter and controller, i would use 2 x 0.8 ..
BR,
Erwin
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
27.01.2018, 12:17
(This post was last modified: 27.01.2018, 16:05 by Mr.D.)
Hi Erwin,
I have changed the cable to a EiB Cable (4x0.8mm2), length of cable is 30-40 cm.
The wiring is as follows:
Spacelynk iEM3150
D1 D1
D0 D0
0V 0V
gnd(RS232) The symbol is a circle with 2 lines through
There are no scripts running that is requesting or polling information from the modbus.
I have restarted the SpaceLynk to make sure there are no other double scripts running.
Despite this, still the following errors in the log:
Schneider (RTU slave 2) read failed: Response not from requested slave
Schneider (RTU slave 2) read failed: Operation timed out
Schneider (RTU slave 2) read failed: Invalid data
Schneider (RTU slave 2) read failed: Invalid CRC
Scriptname in the log is "modbus"
These two errors do not have the same timestamp, it could be many minutes between "events"
Any idea?
BR,
Mr.D
Posts: 1764
Threads: 6
Joined: Jul 2015
Reputation:
117
Hi,
Try with just D0 and D1 connected.
BR,
Erwin
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
28.01.2018, 09:55
(This post was last modified: 29.01.2018, 12:27 by Mr.D.)
Hi,
Disconnected the other wires and just used the D1 and D0.
Still errors
I have reset the iEM3150, but still no change.
I have restarted the SpaceLynk several times.... no effect.
One thing that might be worth mentioning is that after I updated to SpaceLynk version 2.1.1 I am no longer able to download the profile that belongs to iEM3150 in the modbus settings. When trying to download I get 404 Not found....?
I am able to create a new device with that profile, but the Jason-file is not available...
BR,
Mr.D
EDIT: After just connecting D0 and D1 I only seem to be getting the following two errors:
Schneider (RTU slave 2) read failed: Response not from requested slave
Schneider (RTU slave 2) read failed: Operation timed out
So a slight improvement, but still not there... The majority of the errors are the "Response not from requested slave"...
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
Hi,
I am wondering if this started happening after upgrading from 2.0.1 to 2.1.1...
Others have had this issue before.
https://forum.logicmachine.net/showthread.php?tid=670
Any thoughts?
BR,
Mr.D
Posts: 1764
Threads: 6
Joined: Jul 2015
Reputation:
117
29.01.2018, 20:13
(This post was last modified: 29.01.2018, 20:13 by Erwin van der Zwart.)
Hi,
I did a small test on a iEM device and FW 2.1.1, and i get same message. I have reported it to development.
BR,
Erwin
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
Hi Erwin,
Thanks! This has been driving me crazy!
Glad to hear its a system bug, and not an amateur bug on my side
BR,
Mr.D
Posts: 169
Threads: 58
Joined: Oct 2017
Reputation:
0
Hi Erwin, hi Danielsen,
May I suggest you test I add two bus polarization resistors ?
https://www.schneider-electric.fr/fr/faqs/FA22821/
I have not tested this solution yet, but it has been indicated recently to me by the Schneider Electric Customer Care Center.
Note: I had the same CRC problem with a Modbus iEM3155 on HomeLYnk, but I solved 90% of this malfunction by just increasing the POL and the tiemout a little bit.
BR,
Dominique
Posts: 136
Threads: 18
Joined: Apr 2017
Reputation:
1
13.03.2018, 13:07
(This post was last modified: 13.03.2018, 13:08 by Mr.D.)
I am still experiencing this issue... and I am pretty sure it came when I updated from version 2.0.1... So I think its more of a software issue.
BR,
Mr.D
Posts: 74
Threads: 21
Joined: Sep 2016
Reputation:
0
Wondering if this was the same issue I had earlier? I returned the HVAC Modbus gateway since I didn't manage to get it work properly.
https://forum.logicmachine.net/showthread.php?tid=447
Posts: 68
Threads: 3
Joined: Jun 2016
Reputation:
0
(18.04.2018, 12:01)sx3 Wrote: Wondering if this was the same issue I had earlier? I returned the HVAC Modbus gateway since I didn't manage to get it work properly.
https://forum.logicmachine.net/showthread.php?tid=447
Hi,
A bug that disable possibility to import new profile is is known in FW 2.1.1
I'm not aware of issue with modbus, but have tested it since will check with the team and Erwin what's the status of this.
I think a fixed FW is ongoing and will be available 'soon'
@sx3, I don't think you problem is the same, it was long time ago (topic is from 216) and FW 2.1.1 as been release just few weeks/month ago.
Posts: 55
Threads: 18
Joined: Jun 2017
Reputation:
1
@Mr.D have you solved your failure in communications ?!
I have the same issue with VFDs.
Does the SpaceLynk has polarization resistors on the RS485 port ?!
Thank you
|