DALI on LM5
I have just migrated whole project from LM4 to LM5, and my DALI feedbacks stopped working.
All the commands go through - all the lamps go on/off and dimms with no problem, but when queryingactual to read the status i get such error messages:
Event for DALI READ ALL (15/7/3) 22.12.2016 15:51:10 * string: rx error
script:
require('user.dali')
res, err = dalicmd('internal', 'queryactual', { addrtype = 'short', address = 0 })
if res then
   log(res:byte())
   log(err)
when querying any other address i get:
Event for DALI READ ALL (15/7/3) 22.12.2016 15:52:44 * string: reply timeout
When querying all the ballast it's the same:
Event for DALI READ ALL (15/7/3) 22.12.2016 15:54:08 * string: reply timeout
script:
res, err = dalicmd('internal', 'queryshortaddr', { addrtype = 'broadcast' })
if res then
   log(res:byte())
   log(err)
Then i tried scanning through devices and after scan 16 of connected ballasts has disappeared, i cannot detect them again. They were visible before the scan.
Tried rebooting LM, turning off power supply of DALI line.
What else should i try?
Holidays are coming and customer is getting angry. Please help Smile
If You can call me on +370 600 31726
or e-mail directly to l.korsakas@bustoautomatika.lt
Thanks to Edgars, https://dl.openrb.com/lm-16.12-imx6/pkg/...2_imx6.ipk this package solved it.
I'm having the same issue here..
I get "tx error" as well as "rx error" alternatively, I have a LM5p DW1 New CPU with the 20180828 version FW.
The fix file is not available and I presume it wouldn't work either with the version I have.
Thanks..
This bug should be fixed in this FW but all the packages are here https://dl.openrb.com/lm-18-imx6/pkg/
The "rx error" appears when I do a "queryactual" to certain groups, in one LM the error shows on the groups 1 and 2, and in the other LM groups 2 and 3 fails.
In each LM I have 7 Dali groups assigned, the rest of the querys work fine.
tried to reinstall the packages but there is no change.. the error continues.
Do you do it to a group or to a individual ballast?
(29.11.2018, 16:05)Daniel. Wrote: Do you do it to a group or to a individual ballast?
To groups, I made a tool to add and delete ballasts to groups, each ballast only has 1 group assigned, and the other groups respond fine to the query, the groups not assigned return a timeout, but I don't care about them..
I use groups because the customer didn't like the effect when sending a command to each ballast at a different time...
I don't think this should work to a group. What value would you receive when lights can have different values in a group?
This works fine
require('user.dali') res, err = dalicmd('internal', 'queryactual', { addrtype = 'short', address = 0 }) -- read ok if res then  value = res:byte() end log(value)
You are right, if the values are different, it should give me an error but if the value is the same shouldn't be a problem, also the devices are the same model..
ignoring the query actual to a group, how could I get the status of a group then? making a query to each ballast and making an average of the ballasts of the group?
(29.11.2018, 16:24)Morpheus09 Wrote: You are right, if the values are different, it should give me an error but if the value is the same shouldn't be a problem, also the devices are the same model..
In KNX dali gateways they select one light in a group and they just query one ballast.  If you control them all together then this is enough.