Gateway Modbus RTU to Modbus TCP
I have 4 meters connected by Modbus RTU (attachment).
I would like that the Logic Machine works as a Modbus TCP Slave with this 4 meters and with same ID and registers, and then connect to other device. I.e. the Logic Machine works as a Gateway Modbus RTU to Modbus TCP.
Best regards,
This is not possible with default Modbus TCP slave as it only supports one slave ID / one set of registers. One solution is to use single slave ID but different registers addresses for each RTU slave.
Will it be possible to program the LogicMachine so that the meter 1 will use  Modbus TCP slave register 1-100, meter 2 register 101-200 ........?
The Modbus TCP slave exampel only shows register starting from 1.
An exampel/instructions where defined registerts are set would be great!
Actual Modbus addressing starts from 0. Documentation for some devices have addressing starting from 1 which creates confusion.
Here's modified slave script where you can specify addresses directly and there can be gaps in register map, for example: 0..15 for meter 1; 100..115 for meter 2 etc.
This script supports 16-bit values only. If only one way communication is needed (Modbus values are read-only) then it can be modified to support 32-bit and 64-bit values internally without additional scripts for splitting values into 16-bit parts.
12345678910111213141516171819202122232425262728293031323334353637383940414243444546474849505152535455565758596061626364656667686970717273747576777879808182838485868788
if not mb then   require('luamodbus')   -- list of coil mapping, register mapping and register data types   coils, registers, regdt = {}, {}, {}   -- coil definition   coils[ 0 ] = '1/1/1'   coils[ 1 ] = '1/1/2'   -- register definition   registers[ 0 ] = '2/2/2'   regdt[ 0 ] = dt.int8      registers[ 1 ] = '2/2/3'   regdt[ 1 ] = dt.uint16   -- knx group write callback   function knxgroupwrite(event)     local value     -- try to find matching coil     for id, addr in pairs(coils) do       if event.dst == addr then         value = busdatatype.decode(event.datahex, dt.bool)         mb:setcoils(id, value)       end     end     -- try to find matching register     for id, addr in pairs(registers) do       if event.dst == addr then         value = busdatatype.decode(event.datahex, regdt[ id ])         mb:setregisters(id, value)       end     end   end   -- coil write callback   function mbwritecoils(coil, value)     local addr = coils[ coil ]     if addr then       grp.write(addr, value, dt.bool)     end   end   -- register write callback   function mbwriteregisters(register, value)     local addr = registers[ register ]     if addr then       grp.write(addr, value, regdt[ register])     end   end   -- knx group monitor, handles group writes   busclient = require('localbus').new(0.1)   busclient:sethandler('groupwrite', knxgroupwrite)   -- modbus slave, listen on all interfaces and default port 502   mb = luamodbus.tcp()   mb:open('0.0.0.0', 502)   -- setting slave id is optional   -- mb:setslave(1)   mb:setreceivetimeout(0.1)   mb:setmapping(table.maxn(coils) + 1, 0, table.maxn(registers) + 1, 0)   -- init coils   for id, addr in pairs(coils) do     value = grp.getvalue(addr)     mb:setcoils(id, value)   end   -- init registers   for id, addr in pairs(registers) do     value = grp.getvalue(addr)     mb:setregisters(id, value)   end   -- set callbacks for coil and register write   mb:setwritecoilcb(mbwritecoils)   mb:setwriteregistercb(mbwriteregisters) end -- handle modbus and knx mb:handleslave() busclient:step()
