Modbus register write command
I'm writing the modbus interface to Daikin VRF. I have finished and checked with the virtual modbus slave software with the input register with the modbus profile that i create as follow.
  "manufacturer": "Daikin",
  "description": "Daikin VRV 1-00",
  "mapping": [
{ "name": "1-00 A/C Control-Read", "bus_datatype": "bool", "type": "inputregister", "address": 2001, "writable": 0, "datatype": "uint16", "value_bitmask": 0x01, "value_custom": {"0": "Off", "1": "On" } },
{ "name": "1-00 A/C Control-Write", "bus_datatype": "bool", "type": "register", "address": 2001, "writable": true, "datatype": "uint16", "value_bitmask": 0x01, "value_custom": {"0": "Off", "1": "On" } },
{ "name": "1-00 Swing-Read", "bus_datatype": "uint16", "type": "inputregister", "address": 2001, "writable": 0, "datatype": "uint16", "value_bitmask": 0x700, "value_custom": {"0": "P0", "1": "P1", "2": "P2", "3": "P3", "4": "P4", "6": "Swing stop", "7": "Swing on" } },
{ "name": "1-00 Swing-Write", "bus_datatype": "uint16", "type": "register", "address": 2001, "writable": true, "datatype": "uint16", "value_bitmask": 0x700, "value_custom": {"0": "P0", "1": "P1", "2": "P2", "3": "P3", "4": "P4", "6": "Swing stop", "7": "Swing on" } },
{ "name": "1-00 Fan Speed-Read", "bus_datatype": "uint16", "type": "inputregister", "address": 2001, "writable": 0, "datatype": "uint16", "value_bitmask": 0x7000, "value_custom": {"1": "Low", "3": "Medium", "5": "High" } },
{ "name": "1-00 Fan Speed-Write", "bus_datatype": "uint16", "type": "register", "address": 2001, "writable": true, "datatype": "uint16", "value_bitmask": 0x7000, "value_custom": {"1": "Low", "3": "Medium", "5": "High" } },
{ "name": "1-00 Operation Mode-Read ", "bus_datatype": "uint16", "type": "inputregister", "address": 2002, "writable": 0, "datatype": "uint16", "value_bitmask": 0xF, "value_custom": {"0": "Fan", "1": "Heating", "2": "Cooling", "3": "Auto ", "7": "Dry" } },
{ "name": "1-00 Operation Mode-Write ", "bus_datatype": "uint16", "type": "register", "address": 2002, "writable": true, "datatype": "uint16", "value_bitmask": 0xF, "value_custom": {"0": "Fan", "1": "Heating", "2": "Cooling", "3": "Auto ", "7": "Dry" } },
{ "name": "1-00 Filter Alarm-Read ", "bus_datatype": "bool", "type": "inputregister", "address": 2002, "writable": 0, "datatype": "uint16", "value_bitmask": 0xF0, "value_custom": {"0": "Normal", "1": "Alarm", "2": "Alarm", "3": "Alarm", "4": "Alarm", "5": "Alarm", "6": "Alarm", "7": "Alarm", "8": "Alarm", "9": "Alarm", "10": "Alarm", "11": "Alarm", "12": "Alarm", "13": "Alarm", "14": "Alarm", "15": "Alarm" } },
{ "name": "1-00 Filter Alarm-Write ", "bus_datatype": "bool", "type": "register", "address": 2002, "writable": true, "datatype": "uint16", "value_bitmask": 0xF0, "value_custom": {"0": "Normal", "1": "Alarm", "2": "Alarm", "3": "Alarm", "4": "Alarm", "5": "Alarm", "6": "Alarm", "7": "Alarm", "8": "Alarm", "9": "Alarm", "10": "Alarm", "11": "Alarm", "12": "Alarm", "13": "Alarm", "14": "Alarm", "15": "Alarm" } },
{ "name": "1-00 Room Temperature Setpoint-Read", "bus_datatype": "float16", "type": "inputregister", "address": 2003, "writable": 0, "datatype": "int16", "value_multiplier": 0.1, "units": "°C" },
{ "name": "1-00 Room Temperature Setpoint-Write", "bus_datatype": "float16", "type": "register", "address": 2003, "writable": true, "datatype": "int16", "value_multiplier": 0.1, "units": "°C" },
{ "name": "1-00 Actual Room Temperature", "bus_datatype": "float16", "type": "inputregister", "address": 2005, "writable": 0, "datatype": "int16", "value_multiplier": 0.1, "units": "°C" }
All "inputregister" are working fine with bit mask, however all failed in command output.
I have check the previous post that the Bitmasks are supported for reading only. How can I write script for bitmasks writing?
I use 1/1/1 for on/off, 1/1/2 for fan direction and 1/1/3 for fan speed. The protocol table for those points is attached.
Thanks in advance.
Hi, Input registers are read only anyway. Check if they can be written at all. If yes fallow this
https://forum.logicmachine.net/showthrea...5#pid11915
You will need a script to calculate final value by combining 3 objects together. Just make sure to use different group addresses for status and control otherwise you can produce an infinite loop.
onoff = grp.getvalue('1/1/1') -- fan on/off direction = grp.getvalue('1/1/2') -- fan direction speed = grp.getvalue('1/1/3') -- fan speed value = bit.bor(   onoff and 1 or 0,   bit.lshift(bit.band(direction, 0x07), 8),   bit.lshift(bit.band(speed, 0x07), 12) ) grp.update('1/1/4', value)
(12.02.2020, 08:15)admin Wrote: You will need a script to calculate final value by combining 3 objects together. Just make sure to use different group addresses for status and control otherwise you can produce an infinite loop.
Thanks so much. I will check it
How to do AC on/off , fan speed and fan direction by using event script
Add TAG to the 3 input groups and create event script triggered by this tag.
(13.04.2022, 07:48)Daniel Wrote: Add TAG to the 3 input groups and create event script triggered by this tag.
Can you clarify this place for me?
I don't know how to do this?
All grp.getvalue objects in this scripts are inputs and they must have the TAG added. Later under Scripting, create event script which will be trigerred by this TAG you just created on input objects.
PS. bit mask write is supported on modbus profile now.
You need to add "write_bitmask": true to relevant mapping entries.