This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Modbus datapoint type
#1
Hi
I have a De Dietrich air conditioning machine and I need to read the values from the attached table.

When I am in the Modbus tab and in the option to read address, what type of data do I choose?

Sometimes it gives me absurd values always starting from Holding Register.

Thanks in advance.

Attached Files Thumbnail(s)
   
Reply
#2
Uint32, the data may need some conversion like multiply by X, Play with the read swap too.
Also try subtracting register nr by 1 as we start count from zero and some from 1.
------------------------------
Ctrl+F5
Reply
#3
(23.11.2020, 16:32)Daniel. Wrote: Uint32, the data may need some conversion like multiply by X, Play with the read swap too.
Also try subtracting register nr by 1 as we start count from zero and some from 1.