The following scripts integrate Paradox EVO192 security panel. Paradox PRT3 printer module is used to connect the security panel to LM5 through RS232 serial port.
Thanks our forum member rebooter for contribution!
guardZoneStatus library:
function guardzonefunction(zonenumber, zonestatus)
guardZones = {
[255255] = 'An empty zone has arrived',
[01] = 'The main entrance. Motion Sensor.',
[02] = 'The cabinet. Motion Sensor.',
[03] = 'The garage. Motion Sensor.',
[04] = 'The stairs. Motion Sensor.',
[05] = 'The living room. Motion Sensor.',
[06] = 'The dining room. Motion Sensor.',
[07] = 'The kitchen. Motion Sensor.',
[08] = 'Garage entrance. Motion Sensor.',
[09] = 'The main entrance. Window Break Sensor ',
[10] = 'The cabinet. Window Break Sensor ',
[11] = 'The garage. Window Break Sensor ',
[13] = 'Living room. Window Break Sensor ',
[14] = 'Dining room. Window Break Sensor ',
[15] = 'The kitchen. Window Break Sensor ',
[16] = 'The garage door. Reed switch ',
[17] = 'The main entrance. Reed switch ',
[18] = 'Dining room. Curtain',
[19] = 'Boiler room. Motion Sensor.',
[20] = 'The boiler room. Window jammer
[21] = 'Cinema hall. Motion Sensor',
[22] = 'Pantry. Motion Sensor',
[24] = 'SPA room. Motion Sensor',
[25] = 'Children's 1. Motion sensor',
[26] = 'Hall 2 floor. Motion Sensor.',
[27] = 'Children's 2. Motion sensor',
[28] = 'Master bedroom. Motion Sensor',
[30] = 'Pajar basement',
[31] = 'Fire 1st floor',
[32] = 'Fire 2nd floor',
[33] = 'Fire Sauna',
[34] = 'Fire attic',
[35] = 'Server fire',
[36] = 'Under the stairs',
[50] = 'House is armed',
[51] = 'House is disarmed',
-- Arming with mast
zonename = guardZones[zonenumber]
-- log ("Zone Nr triggered: "..zonenumber.." status: "..zonestatus.." "..zonename)
-- log(zonename)
-- log(zonestatus)
-- log(guardZones[zonenumber])
if zonestatus == 'closed' then
status = 1
elseif zonestatus == 'opened' then
status = 0
if zonenumber == 1 then
grp.update('8/0/1', status)
elseif zonenumber == 2 then
-- zonename = guardZones[zonenumber]
grp.update('8/0/2', status)
elseif zonenumber == 3 then
grp.update('8/0/3', status)
elseif zonenumber == 4 then
grp.update('8/0/4', status)
elseif zonenumber == 5 then
grp.update('8/0/5', status)
elseif zonenumber == 6 then
grp.update('8/0/6', status)
elseif zonenumber == 7 then
grp.update('8/0/7', status)
elseif zonenumber == 8 then
grp.update('8/0/8', status)
elseif zonenumber == 9 then
grp.update('8/0/9', status)
elseif zonenumber == 10 then
grp.update('8/0/10', status)
elseif zonenumber == 11 then
grp.update('8/0/11', status)
elseif zonenumber == 13 then
grp.update('8/0/13', status)
elseif zonenumber == 14 then
grp.update('8/0/14', status)
elseif zonenumber == 15 then
grp.update('8/0/15', status)
elseif zonenumber == 16 then
grp.update('8/0/16', status)
elseif zonenumber == 17 then
grp.update('8/0/17', status)
elseif zonenumber == 18 then
grp.update('8/0/18', status)
elseif zonenumber == 19 then
grp.update('8/0/19', status)
elseif zonenumber == 20 then
grp.update('8/0/20', status)
elseif zonenumber == 21 then
grp.update('8/0/21', status)
elseif zonenumber == 22 then
grp.update('8/0/22', status)
elseif zonenumber == 24 then
grp.update('8/0/24', status)
elseif zonenumber == 25 then
grp.update('8/0/25', status)
elseif zonenumber == 26 then
grp.update('8/0/26', status)
elseif zonenumber == 27 then
grp.update('8/0/27', status)
elseif zonenumber == 28 then
grp.update('8/0/28', status)
elseif zonenumber == 30 then
grp.update('8/0/30', status)
elseif zonenumber == 31 then
grp.update('8/0/31', status)
elseif zonenumber == 32 then
grp.update('8/0/32', status)
elseif zonenumber == 33 then
grp.update('8/0/33', status)
elseif zonenumber == 34 then
grp.update('8/0/34', status)
elseif zonenumber == 35 then
grp.update('8/0/35', status)
elseif zonenumber == 36 then
grp.update('8/0/36', status)
-- process the status of security panel
-- if armed then switch off lights in whole house
elseif zonenumber == 50 then
if grp.getvalue('0/5/8') == false then
-- grp.update('0/5/5', status) --lights off
grp.update('0/5/8', status) --security panel status
elseif zonenumber == 51 then
if grp.getvalue('0/5/8') then
elseif zonenumber == 255255 then
log("An empty zone has arrived")
end --if zonenumber
RS232 communication script:
require('user.guardZoneStatus')
if not port then
require('serial')
port = serial.open('/dev/RS232', { baudrate = 9600, parity = 'none', databits = '8', stopbits = '1'})
port:flush()
line = ''
char = port:read(1, 1)
if char then
if char == '\r' then
line = line:trim()
--log(line)
-- mail('info@something.com', 'Installation X', line)
-- loghex(line)
zone = tonumber(string.sub(line,-2))
if zone == nil then
zone = 255255
-- log("An empty zone has arrived")
-- if (zone > 1) or (zone <37 ) then
if (string.match(line,'opened')) == ('opened') then
zoneStatus = 'opened'
armstatus = grp.getvalue('0/5/8') --reading current status of security system
-- log(armstatus)
if armstatus == true then
grp.update('0/5/8', false) -- write those which are not armed
zoneStatus = 'closed'
end -- string.match
-- parsing logs for setting to alarm
if (string.match(line,'Arming')) == ('Arming') then
zone = 50
-- elseif (string.match(line,' in')) == (' in') then
-- zoneStatus = 'closed'
-- zone = 50
elseif (string.match(line,'ode entere')) == ('ode entere') then
zone = 51
end -- string.match
guardzonefunction(zone,zoneStatus)
-- end -- test for zone nember 1 - 36
line = ''
line = line .. char
end -- if char '\r'
08.07.2020, 10:50 (This post was last modified: 08.07.2020, 10:59 by fleeceable.)
Hello!
Here is my updated communication script. Maybe this helps someone...
It allows to see zone status, get info about areas (if there is trouble in some area and if area is open or not), arm/disarm etc...
Also it polls every minute area status.
require('user.guardAreaStatus')
if not port then
require('serial')
port:flush()
line = ''
control_house_security_ga = '10/1/0' --area1 security status group address
control_woodstorage_security_ga = '10/1/1' --area2 security status group address
security_code = '1234'
--log(char)
if char then
line = line:trim()
--log(line)
event = string.sub(line,1,2)
-- log(event)
if event == 'G0' then
eventnr = tonumber(string.sub(line,6,-5))
area = tonumber(string.sub(line,10,-1))
eventngr = tonumber(string.sub(line,2,4))
if zone == nil then
zone = 255255
guardzonefunction(eventngr,eventnr,area)
elseif event == 'RA' then
area = tonumber(string.sub(line,3,5))
securitystatus_1 = string.sub(line,6,6)
areastatus_1 = string.sub(line,7,7)
areastatus_2 = string.sub(line,8,8)
areastatus_3 = string.sub(line,9,9)
areastatus_4 = string.sub(line,10,10)
areastatus_5 = string.sub(line,11,11)
areastatus_6 = string.sub(line,12,12)
guardareafunction(area,securitystatus_1,areastatus_1,areastatus_2,areastatus_3,areastatus_4,areastatus_5,areastatus_6 )
line = ''
line = line .. char
request = grp.getvalue('32/5/0') --scheduled script changes object to true every minute. !!!ADD SCHEDULED SCRIPT!!!
if request then
port:write('RA001\r') --send area1 status request command
os.sleep(0.5)
port:write('RA002\r') --send area2 status request command
grp.update('32/5/0', false)
house_arm_disarm = grp.getvalue(control_house_security_ga) --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
if house_arm_disarm == 1 then
port:write('AA001A'..security_code..'\r')
grp.update(control_house_security_ga, 0)
elseif house_arm_disarm == 2 then
port:write('AA001F'..security_code..'\r')
elseif house_arm_disarm == 3 then
port:write('AA001S'..security_code..'\r')
elseif house_arm_disarm == 4 then
port:write('AA001I'..security_code..'\r')
elseif house_arm_disarm == 5 then
port:write('AD001'..security_code..'\r')
woodstorage_arm_disarm = grp.getvalue(control_woodstorage_security_ga) --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
if woodstorage_arm_disarm == 1 then
port:write('AA002A'..security_code..'\r')
grp.update(control_woodstorage_security_ga, 0)
elseif woodstorage_arm_disarm == 2 then
port:write('AA002F'..security_code..'\r')
elseif woodstorage_arm_disarm == 3 then
port:write('AA002S'..security_code..'\r')
elseif woodstorage_arm_disarm == 4 then
port:write('AA002I'..security_code..'\r')
elseif woodstorage_arm_disarm == 5 then
port:write('AD002'..security_code..'\r')
User library:
Script name: guardAreaStatus
function guardareafunction(areanumber, areastatus, areastatus1, areastatus2, areastatus3, areastatus4, areastatus5, areastatus6 ) --what must be process RA001DOONOOO; RA - Request area; 001 - Area number; D - Disarmed/Armed/Force armed/Stay armed/Instant armed; O - Zone in memory/Ok; O - Troube/Ok; N - Not ready/Ok; O - In programming/Ok; O - In alarm/Ok; O - Strobe/Ok
house_area_status_ga = '10/0/0'
woodstorage_area_status_ga = '10/0/1'
house_area_trouble_ga = '10/3/0'
woodstorage_area_trouble_ga = '10/3/1'
house_area_not_ready_ga = '10/3/2'
woodstorage_area_not_ready = '10/3/3'
house_area_alarm_ga = '10/2/0'
woodstorage_area_alarm_ga = '10/2/1'
if areastatus == 'D' then
if areanumber == 1 then
grp.write(house_area_status_ga, 0)
elseif areanumber == 2 then
grp.write(woodstorage_area_status_ga, 0)
elseif areastatus == 'A' then
grp.update(house_area_status_ga, 1)
grp.update(woodstorage_area_status_ga, 1)
elseif areastatus == 'F' then
grp.update(house_area_status_ga, 2)
grp.update(woodstorage_area_status_ga, 2)
elseif areastatus == 'S' then
grp.update(house_area_status_ga, 3)
grp.update(woodstorage_area_status_ga, 3)
elseif areastatus == 'I' then
grp.update(house_area_status_ga, 4)
grp.update(woodstorage_area_status_ga, 4)
if areastatus2 == 'T' then
grp.update(house_area_trouble_ga, true)
grp.update(woodstorage_area_trouble_ga, true)
elseif areastatus2 == 'O' then
grp.update(house_area_trouble_ga, false)
grp.update(woodstorage_area_trouble_ga, false)
if areastatus3 == 'N' then
grp.update(house_area_not_ready_ga, true)
grp.update(woodstorage_area_not_ready, true)
elseif areastatus3 == 'O' then
grp.update(house_area_not_ready_ga, false)
grp.update(woodstorage_area_not_ready, false)
if areastatus5 == 'A' then
grp.update(house_area_alarm_ga, true)
grp.update(woodstorage_area_alarm_ga, true)
elseif areastatus5 == 'O' then
grp.update(house_area_alarm_ga, false)
grp.update(woodstorage_area_alarm_ga, false)
Script name: guardZoneStatus
function guardzonefunction( eventgroup,eventnumber,areanumber)
guardZones = {
[01] = 'Tehnoruum PIR.',
[02] = '1k Trepihall PIR.',
[03] = 'Kontor PIR.',
[04] = 'Esik PIR.',
[05] = 'Elutuba PIR.',
[06] = 'Magamistuba PIR.',
[07] = 'Garderoob PIR.',
[08] = 'Kuur PIR.',
[09] = 'Mona PIR ',
[10] = 'Cara PIR ',
[11] = '2k Trepihall PIR ',
[12] = 'Tehnoruumi Suits ',
[13] = '1 Trepihall Suit ',
[14] = 'Kontori Suits ',
[15] = 'Esiku Suits ',
[16] = 'Elutoa Suits ',
[17] = 'Magamistoa Suits ',
[18] = 'Garderoob Suits',
[19] = 'Mona Suits',
[20] = 'Cara Suits',
[21] = '2 Trepihall Suit',
[22] = '2k Elutoa Suits',
[23] = 'Kuuri Uks',
[24] = 'Kontori Aken',
[25] = 'Peauks',
[26] = 'Köögi Aken.',
[27] = 'Terrassi Uks',
[28] = '1k Vannitoa Uks',
[29] = '1k Vannitoa Aken',
[30] = 'Magamistoa Aken',
[31] = 'Kuuri Aken',
[32] = 'Mona 1 Aken',
[33] = 'Cara 1 Aken',
[34] = '2k Vannitoa Aken',
[35] = '2k Elutuba M',
[36] = 'Mona 2 Aken',
[37] = 'Cara 2 Aken',
[38] = 'Valvekilp',
house_area_exit_delay_ga = '10/0/2'
house_area_entry_delay_ga = '10/0/3'
woodstorage_area_exit_delay_ga = '10/0/4'
woodstorage_area_entry_delay_ga = '10/0/5'
if eventgroup == 0 or eventgroup == 1 then
if eventgroup == 0 then
grp.update('10/4/'..eventnumber, false)
elseif eventgroup == 1 then
grp.update('10/4/'..eventnumber, true)
elseif eventgroup == 13 then
grp.update(house_area_status_ga, 0)
grp.update(woodstorage_area_status_ga, 0)
elseif eventgroup == 64 then
if eventnumber == 0 then
elseif eventnumber == 1 then
elseif eventnumber == 2 then
elseif eventnumber == 3 then
elseif eventnumber == 4 or eventnumber == 5 or eventnumber == 6 or eventnumber == 7 then
elseif eventgroup == 65 then
grp.update(house_area_exit_delay_ga, true)
grp.update(woodstorage_area_exit_delay_ga, true)
grp.update(house_area_entry_delay_ga, true)
grp.update(woodstorage_area_entry_delay_ga, true)
elseif eventnumber == 0 then
grp.update(house_area_entry_delay_ga, false)
grp.update(house_area_exit_delay_ga, false)
grp.update(woodstorage_area_entry_delay_ga, false)
grp.update(woodstorage_area_exit_delay_ga, false)
Resident script for communication check (EVO192 Communication check, sleep interval 10s):
last_timestamp = grp.find("10/0/0").updatetime --Area1 status (status is polled every minute from security system)
communication_error = grp.getvalue('10/3/4')
now = os.microtime()
if (now - last_timestamp) >= 120 then --if object hasn't updated on last 120s then generate communication error
if communication_error == false then
grp.update('10/3/4', true)
if grp.getvalue('10/3/4')==true then
grp.update('10/3/4', false)
18.07.2020, 14:37 (This post was last modified: 16.04.2024, 18:58 by fleeceable.)
Another update to get integration done about 1 minute.
Now my script reads out all arealabels and zone labels (You don't need to know anything about EVO program). Also creates automatically group objects. I tested it couple days ago in my new project and really, integration takes about 1-2 minutes.
What you probably need to do is edit zone labels to more understandable form (paradox allows enter only 16 characters for area and zone name).
Program needs one main group address range (example 10/x/x)
Group address structure is like this:
security_main_ga = '10/' --'3-level' = main/middle/sub. Make sure that 10/0/0 - 10/7/X group addresses are not used. System creates objects automatically.
10/0/1 - Area 1 security status [0-DISARMED, 1-ARMED, 2-FORCE ARMED, 3-STAY ARMED, 4-INSTANT ARMED]
10/0/8 - Area 8 security status
10/0/11 - Area 1 exit delay
10/0/18 - Area 8 exit delay
10/0/21 - Area 1 entry delay
10/0/28 - Area 8 entry delay
10/0/31 - Area 1 alarm status
10/0/38 - Area 8 alarm status
10/0/41 - Area 1 trouble
10/0/48 - Area 8 trouble
10/0/51 - Area 1 not ready
10/0/58 - Area 8 not ready
10/1/1 - Area 1 control [1-ARM, 2-FORCE ARM, 3-STAY ARM, 4-INSTANT ARM, 5-DISARM]
10/1/8 - Area 8 control
10/2/1 - Zone 1 status
10/2/xxx - Zone xxx status
All what you need to change is in resident script (group addresses).
require('user.guardAreaLabels')
require('user.guardZoneLabels')
command_enum = {
[1] = 'A',
[2] = 'F',
[3] = 'S',
[4] = 'I',
if not port then
require('serial')
port:flush()
line = ''
request_area_status_ga = '32/5/0' --Create scheduled script for this one. Write true every minute.
request_zone_labels_ga = '32/5/3' --You need to change this to true only one time or if security zones are changed.
--This also activates group address generation.
--Make sure that zone label is not "Zone 001, Zone 002 etc because these zone names gonna be ignored.
request_area_labels_ga = '32/5/4' --You need to change this to true only one time or if security areas are changed.
--Make sure that area label is not "Area 001, Area 002 etc because these area names gonna be ignored.
request_zone_name_count = 50 --how many zones will be scanned to get zone labels.
active_areas = 1 --How many areas are polled periodically. Starts on first area.
--log(char)
if char then
line = line:trim()
log(line)
-- log(event)
guardzonefunction(eventngr,eventnr,area,security_main_ga)
guardareafunction(area,securitystatus_1,areastatus_1,areastatus_2,areastatus_3,areastatus_4,areastatus_5,areastatus_6,security_main_ga )
elseif event == 'AL' then
name = string.sub(line,6,16)
guardarealabelfunction(area, name,security_main_ga)
elseif event == 'ZL' then
zone = tonumber(string.sub(line,3,5))
guardzonelabelfunction(zone, name,security_main_ga)
line = ''
line = line .. char
request = grp.getvalue(request_area_status_ga) --scheduled script changes object to true every minute
if request then
for i = 1, active_areas, 1 do
port:write('RA00'.. i .. '\r') --send area1 status request command
os.sleep(0.2)
if i==active_areas then
grp.update(request_area_status_ga, false)
request_area_names = grp.getvalue(request_area_labels_ga)
if request_area_names then
for i = 1, 8, 1 do
port:write('AL00'..tostring(i)..'\r')
os.sleep(0.2)
grp.update(request_area_labels_ga, false)
request_zone_names = grp.getvalue(request_zone_labels_ga)
if request_zone_names then
for i = 1, request_zone_name_count, 1 do
if i<10 then
port:write('ZL00'..tostring(i)..'\r')
os.sleep(0.2)
port:write('ZL0'..tostring(i)..'\r')
os.sleep(0.2)
grp.update(request_zone_labels_ga, false)
exist = grp.alias(security_main_ga .. '1/' .. i)
if exist ~= nil then
AreaControl = grp.getvalue(security_main_ga .. '1/' .. i) --1-Arm; 2-Force arm; 3-Stay arm; 4-Instant arm; 5-Disarm
if AreaControl ~=0 then
if AreaControl ~= 5 then
port:write('AA00' .. i .. command_enum[AreaControl] .. security_code ..'\r')
grp.update(security_main_ga .. '1/' .. i, 0)
port:write('AD00' .. i .. security_code ..'\r')
User library (guardAreaLabels):
function guardarealabelfunction(areanumber, areaname, security_main_ga)
if areaname ~= ('Area ' .. tonumber(areanumber)) then
for i = 1, 7, 1 do
if i==1 then
exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber))
if exist == nil then
address = grp.create({
datatype = dt.uint8,
address = security_main_ga .. '0/' .. tonumber(areanumber),
name = areaname .. ' security status',
comment = 'Automatically created object - Security Area '.. tonumber(areanumber),
units = '',
tags = { },
elseif i==2 then
exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+10)
datatype = dt.bool,
address = security_main_ga .. '0/' .. tonumber(areanumber)+10,
name = areaname .. ' exit delay',
comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' exit delay',
units = '',
tags = { },
elseif i==3 then
exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+20)
datatype = dt.bool,
address = security_main_ga .. '0/' .. tonumber(areanumber)+20,
name = areaname .. ' entry delay',
comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' entry delay',
units = '',
tags = { },
elseif i==4 then
exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+30)
datatype = dt.bool,
address = security_main_ga .. '0/' .. tonumber(areanumber)+30,
name = areaname .. ' alarm status',
comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' alarm status',
units = '',
tags = { },
elseif i==5 then
exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+40)
datatype = dt.bool,
address = security_main_ga .. '0/' .. tonumber(areanumber)+40,
name = areaname .. ' trouble',
comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' trouble',
units = '',
tags = { },
elseif i==6 then
exist = grp.alias(security_main_ga .. '0/' .. tonumber(areanumber)+50)
datatype = dt.bool,
address = security_main_ga .. '0/' .. tonumber(areanumber)+50,
name = areaname .. ' not ready',
comment = 'Automatically created object - Security Area '.. tonumber(areanumber) .. ' not ready',
units = '',
tags = { },
elseif i==7 then
exist = grp.alias(security_main_ga .. '1/' .. tonumber(areanumber))
address = security_main_ga .. '1/' .. tonumber(areanumber),
name = 'Control ' .. areaname,
comment = 'Automatically created object - Control Security Area '.. tonumber(areanumber),
units = '',
tags = { },
User library (guardAreaStatus):
function guardareafunction(areanumber, areastatus, areastatus1, areastatus2, areastatus3, areastatus4, areastatus5, areastatus6, security_main_ga ) --what must be process RA001DOONOOO; RA - Request area; 001 - Area number; D - Disarmed/Armed/Force armed/Stay armed/Instant armed; O - Zone in memory/Ok; O - Troube/Ok; N - Not ready/Ok; O - In programming/Ok; O - In alarm/Ok; O - Strobe/Ok
grp.write(security_main_ga .. '0/' .. areanumber , 0)
grp.update(security_main_ga .. '0/' .. areanumber , 1)
grp.update(security_main_ga .. '0/' .. areanumber , 2)
grp.update(security_main_ga .. '0/' .. areanumber , 3)
grp.update(security_main_ga .. '0/' .. areanumber , 4)
grp.update(security_main_ga .. '0/' .. areanumber+40 , true)
grp.update(security_main_ga .. '0/' .. areanumber+40 , false)
grp.update(security_main_ga .. '0/' .. areanumber+50 , true)
grp.update(security_main_ga .. '0/' .. areanumber+50 , false)
grp.update(security_main_ga .. '0/' .. areanumber+30 , true)
grp.update(security_main_ga .. '0/' .. areanumber+30 , false)
User library (guardZoneLabels):
function guardzonelabelfunction(zonenumber, zonename, security_main_ga)
exist = grp.alias(security_main_ga .. '2/'.. tonumber(zonenumber))
if zonenumber<10 then
if zonename ~= ('Zone 00' .. tonumber(zonenumber)) then
datatype = dt.bool,
address = security_main_ga .. '2/'.. tonumber(zonenumber),
name = zonename,
comment = 'Automatically created object - Zone '.. tonumber(zonenumber),
units = '',
tags = { },
elseif zonenumber>=10 and zonenumber<100 then
if zonename ~= ('Zone 0' .. tonumber(zonenumber)) then
datatype = dt.bool,
name = zonename,
units = '',
tags = { },
elseif zonenumber>=100 then
if zonename ~= ('Zone ' .. tonumber(zonenumber)) then
datatype = dt.bool,
name = zonename,
units = '',
tags = { },
After you request area and zone names, give it some time to scan and create group objects. Mine needed about 15-20 seconds (1 area, 50 zones)...
All objects what are created automatically they have also object comment "Automatically created object - Security Area X", "Automatically created object - Zone XX" etc..
01.12.2020, 21:05 (This post was last modified: 01.12.2020, 21:07 by mishoboss.)
Hi, thank you for this script! I'm investigating the best possible way to integrate a security system with KNX in my next project. Satel has INT-KNX-2, which is great, but it has certain limitations (e.g. only 64 addresses). There are some pricey 3rd party modules for DSC. And there is Paradox with PRT3 and pricey 3rd party modules again, or using Logic Machine alternatively. The last option I like the most, because I'll probably put a Logic Machine into the project anyways.
Two questions:
1. Does this script work with the newer Paradox serial module? PRT3 is now discontinued and replaced.
2. Are zone changes reported imidiately? For example if a motion sensor detects motion, is this reported on the same second?
(01.12.2020, 21:05)mishoboss Wrote: Hi, thank you for this script! I'm investigating the best possible way to integrate a security system with KNX in my next project. Satel has INT-KNX-2, which is great, but it has certain limitations (e.g. only 64 addresses). There are some pricey 3rd party modules for DSC. And there is Paradox with PRT3 and pricey 3rd party modules again, or using Logic Machine alternatively. The last option I like the most, because I'll probably put a Logic Machine into the project anyways.
Two questions:
Hi!
I definitelly should choose LM to integrate security system. You have no limits when using LM. Can program whatever you want.
Answers:
1. I havent tested it but if all commands are the same then it will work.
2. Yes, this is realtime info. In one project I am using movement from security as triger and switch lights when brightness is below setpoint.
(26.06.2021, 05:27)mishoboss Wrote: Hi, is there a way to control Paradox PGMs (outputs)?
I didn't find any straight solution because there is no command to control PGM output directly. PGM output is meant to control via some statements inside paradox.
But, this solution should work (haven't tested it by myself) but paradox uses this solution with RF remotes.
You can try to use utility key and create this kind of configuration (picture 1 attached). I think there is possible to create similar configuration in BabyWare also.
In LM add this code in residential script to test it out:
utility_key1_grp_addr = 'x/x/x' -- turn PGM on group address
utility_key2_grp_addr = 'x/x/x' -- turn PGM off group address
utility_key1 = grp.getvalue(utility_key1_grp_addr) -- PGM on
utility_key2 = grp.getvalue(utility_key2_grp_addr) -- PGM off
if utility_key1==true or utility_key1==1 then
port:write('UK001\r')
grp.update(utility_key1_grp_addr, false)
os.sleep(0.2)
elseif utility_key2==true or utility_key2==1 then
port:write('UK002\r')
grp.update(utility_key2_grp_addr, false)
os.sleep(0.2)
enable log(event) in residential script to see if command is accepted.
Unfortunately there is no request/status command to see what is PGM state.
Hello. Everything is perfect but I see that the connection is through RS-232 port. My initial question is if there is some possibility to manage a alarm central through http connection. This kind of central usually include web server.
Thank you.
ASCII protocol should only contain printable characters. Since you are getting <?> (unprintable character) it means that there's something wrong on the communication level.
11.03.2022, 11:51 (This post was last modified: 11.03.2022, 11:52 by fleeceable.)
You can also try to switch Tx and Rx cables on logic side.
Another way to test that your PRT3 module (and paradox program) works is to use RS232 to USB converter and connect PRT3 to computer. Then use Docklight (https://docklight.de/) program. If all settings are correct you should see some data on Docklight terminal...
I have used that Logic library on 4 sites and all works great.
(11.03.2022, 11:51)fleeceable Wrote: You can also try to switch Tx and Rx cables on logic side.
Problem solved!
It was a bad wire connection inside the DB9 connector. The gnd wire was disconected.
It is hard to understand why Paradox did not include Bypass function on the PRT3.
They have it with the IP module... Everyone should send an update request to Paradox to have it added to the PRT3. It takes numbers to get results.
22.04.2024, 08:47 (This post was last modified: 22.04.2024, 08:48 by mishoboss.)
Hi! Right now the D (disarmed) status is mapped to number 0 and the disarm control is mapped to number 5. I need disarm control and status to be mapped to the same number, for example 5. So I thought it would be easy to remap those here:
grp.update(security_main_ga .. '0/' .. areanumber , 5)
However DISARMED status is still reported as 0 instead of 5 right after disarming, or it's even not reported at all in some cases. I've scheduled a script to call request_area_status_ga = true every minute and this one successfully updates it to 5. So it works, just not right after DISARMING for some reason. All other controls successfully update the status, it's just the disarm one that is the issue. What I'm missing here?
22.04.2024, 10:54 (This post was last modified: 22.04.2024, 10:59 by fleeceable.)
(22.04.2024, 08:47)mishoboss Wrote: Hi! Right now the D (disarmed) status is mapped to number 0 and the disarm control is mapped to number 5. I need disarm control and status to be mapped to the same number, for example 5. So I thought it would be easy to remap those here:
You need to change this to get 5 for disarm:
elseif eventgroup == 5 then -- user code entered on keypad
grp.update(security_main_ga .. '0/' .. areanumber , 0) ------<<<<<CHANGE THIS TO 5
grp.update(security_main_ga .. '0/' .. areanumber+10,false) --reset exit delay
grp.update(security_main_ga .. '0/' .. areanumber+20 , false) --reset entry delay
elseif eventgroup == 13 or eventgroup == 14 then -- disarm with master or user code
Also you don't need to change "command_enum" because that is used only to send right arming command (usual arm, force arm, stay arm etc). If AreaControl variable is 5 then it gonna disarm on either way. Check residential script line 104.