Write Multiple Registers at once
I have a Modbus equipment that requires that 3 continuous registers must be written in the same operation ( Modbus Function Code 16 ).
... {"name":"UI_1 Cmd Modo Func RAW"   ,"bus_datatype":"8","type":"register","datatype":"int16",     "address":33,   "read_swap":"n","writable":1 }, {"name":"UI_1 Cmd Modo Fan RAW"    ,"bus_datatype":"8","type":"register","datatype":"int16",     "address":34,   "read_swap":"n","writable":1 }, {"name":"UI_1 Cmd Setpoint"       ,"bus_datatype":"8","type":"register","datatype":"int16",     "address":35,   "read_swap":"n","writable":1 },
Is this possible to do this ?
Thank you
Datatype define how many registers are read/written. Int16 is one register, int32 two and so on.
(31.12.2020, 11:35)Daniel. Wrote: Datatype define how many registers are read/written. Int16 is one register, int32 two and so on.
Sorry, I think I didn't make myself understood.
I need to write these 3 registers in the same Write Operation ( FC16).
This way writes correctly, but one after the other:
So, you are telling me that if I use just one variable with the "datatype":"int48" will it work ?
Thank you
This is not possible via profile, you have to use a script instead
(31.12.2020, 12:04)admin Wrote: This is not possible via profile, you have to use a script instead
Humm OK
Something like this ?
Have you got some documentation about the writeregisters method ?
require('luamodbus') mb = luamodbus.tcp() mb:open('192.168.0.1', 502) mb:connect() mb:writeregisters(???) mb:close()
I have other TCP slaves via mapper. This script will be Event based. Can the communications work in parallel without trouble ?
Thank you
TCP should be ok this way, for RTU there's proxy library to use scripts together with profiles