26.10.2021, 11:36 (This post was last modified: 26.10.2021, 11:38 by vmic.)
Hi!
I would like to use the LM Lite 5 Power DRĀ as a KNX gateway but unfortunetally I cna; program KNX devices using ETS5 cuase I am receiving some error messages.
I am sending you the images to see . I changed the KNX address of the LM device but still the problem exists.
Any ideas on how to resolve this issue please?
26.10.2021, 18:45 (This post was last modified: 26.10.2021, 19:04 by vmic.)
(26.10.2021, 16:20)Daniel Wrote: Do you have now the zerotier enabled on lm or on your computer? Make sure everything is local. Rebooting ets or even pc might help.
I have ZeroTier both enabled on LM and PC . I made Reboot also on the ETS nad my PC but still the problem exists! I tried another IP KNX interface and everything works great! I don't know what is going on!
(26.10.2021, 18:45)vmic Wrote:
(26.10.2021, 16:20)Daniel Wrote: Do you have now the zerotier enabled on lm or on your computer? Make sure everything is local. Rebooting ets or even pc might help.
I have ZeroTier both enabled on LM and PC . I made Reboot also on the ETS nad my PC but still the problem exists! I tried another IP KNX interface and everything works great! I don't know what is going on!
You have KNX loop in there. You must have more than one IP router connected to the same TP. LM also counts as IP router. I changed on your LM multicast to 224.0.23.13 and all works fine now.