LM5p2-DR internal DALI gateway respond time
Dear Admin,
I actived the internal DALI gateway for LM5p2-DR(Firmware).
During the test, I found that to turn on the lamp(short,add=1) needs 5-6 seconds and full for 3-4 seconds.
I try use Dali command(Resident scripting as below) to shorten the reaction time but no progress.
require('user.dali')
dalicmd( 'internal', 'setdtr', { addrtype = 'short', address = 1, value = 1})
dalicmd( 'internal', 'storefadetime', { addrtype = 'short', address = 1})
dalicmd( 'internal', 'storefaderate', { addrtype = 'short', address = 1})
Any way out if I want to turn on lamp immediately?
And what is the default fade time and fade rate setting for the internal DALI gateway ?
LM5p2-DR Firmware is 20221205(2022-RC1)
Fade time and rate only is a ballast setting. The gateway simply sends either an absolute value (arc) or a relative up/down dimming.
Fade time values (absolute value):
0 = No fade 1 = 0.7 sec 2 = 1.0 sec 3 = 1.4 sec 4 = 2.0 sec 5 = 2.8 sec 6 = 4.0 sec 7 = 5.7 sec 8 = 8.0 sec 9 = 11.3 sec 10 = 16.0 sec 11 = 22.6 sec 12 = 32.0 sec 13 = 45.3 sec 14 = 64.0 sec 15 = 90.5 sec
Fade rate settings (relative dimming):
1 = 357.8 steps/sec 2 = 253.0 steps/sec 3 = 178.9 steps/sec 4 = 126.5 steps/sec 5 = 89.4 steps/sec 6 = 63.3 steps/sec 7 = 44.7 steps/sec 8 = 31.6 steps/sec 9 = 22.4 steps/sec 10 = 15.8 steps/sec 11 = 11.2 steps/sec 12 = 7.9 steps/sec 13 = 5.6 steps/sec 14 = 4.0 steps/sec 15 = 2.8 steps/sec
Hi admin, this info. helps me a lot, thanks!