Hello Dears,
I tried to connect two Modbus outputs to the same GA, but when write only one take the value!
is this the normal situation, or could I use central GA for multiple Modbus outputs?
Best Regards,
Posts: 7766
Threads: 42
Joined: Jun 2015
Reputation:
447
You should be able to map a single object to multiple Modbus data points. Check if you have any relevant entries in the global Error log and Modbus Error log. If you are using Modbus TCP then try enabling the "Persistent connection" mode.
Posts: 321
Threads: 72
Joined: Jan 2021
Reputation:
0
21.03.2023, 15:13
(This post was last modified: 21.03.2023, 15:15 by khalil.)
this what I got in the error log:
Connection failed: connection refused.
while the Modbus connection for this device is active, I don't have any offline devices
this is before enabling the Persistent connection, while didn't try afterward
Best Regards,