Hi admin!
The project I have uses a Canx UIO16 device. After power failure and reboot, the group addresses are not controllable, I have to Write Configuration of the UIO16 device to be able to control the group addresses.
Thank you in advance!
Posts: 5822
Threads: 31
Joined: Aug 2017
Reputation:
266
Please simulate the power failure again and then scan the line and scan the device, see if configuration are there and groups assigned. If not then device need replacement.
------------------------------
Ctrl+F5
Posts: 5822
Threads: 31
Joined: Aug 2017
Reputation:
266
Click here to scan the device, it will read back all settings from the device.
------------------------------
Ctrl+F5
Posts: 5822
Threads: 31
Joined: Aug 2017
Reputation:
266
Contact us via email for a replacement. Attach link to this thread in it.
------------------------------
Ctrl+F5
Posts: 5822
Threads: 31
Joined: Aug 2017
Reputation:
266
(12.06.2023, 07:09)hoangknx Wrote: (19.05.2023, 10:53)aicanx Wrote: (19.05.2023, 08:50)Daniel Wrote: Contact us via email for a replacement. Attach link to this thread in it.
The UIO16 machine has a Scan Device function, sometimes it can be accessed, sometimes it can't. Once I got access to the scanning device, I had to reselect each group address and save it. The error after powering off and on again has been fixed, group addresses work again. Thank you for the very quick response!
Hi daniel, I also have this problem with CanX devies.
If you performed all the tests as described above with same results then fallow the same advice.
------------------------------