23.02.2024, 07:54
I have 3 UH50 heatmeters that is battery operated. They only update data each 15min. What is the correct way to set up LM as GW for these devices?
I use a MBus to RS232 gateway.
MBus and Siemens UH50 meter
23.02.2024, 07:54
23.02.2024, 08:20
Use a scheduled script. Check this guide: https://kb.logicmachine.net/integration/mbus/
26.02.2024, 06:51
That's probably right, but when the meter only sends each 15mn, it is in sleep mode the remaining time. It's turning into quite a challange to sync LM and meter.
26.02.2024, 06:56
M-Bus provides both data and power over two-wire connection. This means that the M-Bus module is permanently powered even though the meter itself uses battery power. You can probably read the data at any time but it won't be real-time measurements.
26.02.2024, 09:06
None of the meters are responding to adress scans eighter.. It was based on that I thought that values only was available every 15min.
26.02.2024, 09:11
Have you configured short address on each meter? M-Bus module might use a different baud rate like 1200 or 4800.
26.02.2024, 12:13
yes, i think so.. strange.. I also have the secondary adresses of the meters, but how does the mbus.scansecondary function work?
i only get this error; Code: 12 attempt to call field 'scansecondary' (a nil value)
stack traceback:
26.02.2024, 12:41
You have outdated firmware.
26.02.2024, 12:45
Code: 1 SW: 20230607
26.02.2024, 12:46
Install 2024 RC1.
18.04.2024, 11:40
(18.04.2024, 11:40)BrentW Wrote:(26.02.2024, 12:45)tomnord Wrote: I got it to work, had some issues with cables. All values ar updatet each 15min, but previous value is stored in mBus buffer. Script below with separated GA's. Code: 12345678910111213141516171819202122232425262728293031323334353637383940414243444546474849505152535455565758596061626364656667686970 -- config init
if not meters then
require('mbus')
-- time to wait between each meter read
sleeptime = 10
-- use /dev/RS232 serial port with 2400 baud rate
mbus.init('/dev/RS232', 2400)
-- meter definition
-- addr - short address
-- id - number from data table where value resides
-- div - optional divisor for convertion to the final value
meters = {
{ ga = '3/0/0', addr = 10, id = 4, div = 10}, -- kW, dpt 14.
{ ga = '3/0/1', addr = 10, id = 2}, -- kWh dpt 12.
{ ga = '3/0/2', addr = 10, id = 5, div = 1000 }, -- m3h dpt 14
{ ga = '3/0/3', addr = 10, id = 6 }, --T1 dpt 12.
{ ga = '3/0/4', addr = 10, id = 7 }, -- T2 dpt 12.
{ ga = '3/1/0', addr = 20, id = 4, div = 10 }, -- kW
{ ga = '3/1/1', addr = 20, id = 2}, -- kWh
{ ga = '3/1/2', addr = 20, id = 5, div = 1000 }, --m3h
{ ga = '3/1/3', addr = 20, id = 6 }, --T1
{ ga = '3/1/4', addr = 20, id = 7 }, --T2
{ ga = '3/2/0', addr = 30, id = 4, div = 10 }, --kW
{ ga = '3/2/1', addr = 30, id = 2}, --kWh
{ ga = '3/2/2', addr = 30, id = 5, div = 1000 }, --m3h
{ ga = '3/2/3', addr = 30, id = 6 }, --T1
{ ga = '3/2/4', addr = 30, id = 7 }, --T2
-- reset meter values on first run
for _, meter in ipairs(meters) do
meter.value = 0
-- read each meter
res = mbus.getdata(meter.addr)
-- read ok
if type(res) == 'table' then
data = res.data[ meter.id ]
value = nil
-- get current value
if type(data) == 'table' then
value = tonumber(data.value)
-- value is valid and different from previous read
if value and meter.value ~= value then
-- apply divisor if set
div = meter.div
dpt = div and dt.float32 or dt.uint32
if div then
value = value / div
-- update group address value
grp.update(meter.ga, value, dpt)
meter.value = value
--log(meter.ga, meter.value, dpt)
-- wait for next read
os.sleep(sleeptime)
01.05.2024, 09:28
Thanks for sending through,
What were the cable issues if you dont mind me asking?
13.05.2024, 12:31