Modbus, getting bits in a register
How can I read out single bits from a 16-bit register? And write the bit to a group address? The modbus addresses in the readcoils function are not the same as for the readinputs addresses.
I also want a tip how I can read signed 16-bit register? (out side air temperature)
Espen Big Grin
If you read a 16 bits integer register you can get back value 0 to 65535, but when this register is used as single bit (not coil) you probably get back only value 0 or 1 out of this register.
To use that value for a 1 bit KNX value you can simply transfer it to boolean by using this:
value = mb:readregisters(123) if value == 0 or value == 1 then  value = toboolean(value)  grp.write('1/1/1', value) end
To set 16 bits register value to 2 byte signed you can use this code:
r1 = mb:readregisters(124) value = lmcore.inttohex(r1, 2) value = knxdatatype.decode(value, dt.int16)
If your register is not a bitmask but a single bit you can write it directly to a boolean object, any numeric value other than 0 will be treated as true. As for reading int16, you can use this:
value = mb:readregistervalue(123, 'int16')
My 16-bit register is a bitmask, e.g.:
Input register 3x0006 consists of:
Bit 0 = Dampers open
Bit 1 = Fire dampers open
Bit 2 = Fire dampers closed
Bit 3 = Status feedback pump
Etc.
I'm interested in getting out the status of a single bit within a register. Not the whole register acting as a bit, 0 or 1.
Is it possible?
You can use this helper function:
function getbit(value, nr)   value = bit.rshift(value, nr)   return bit.band(value, 1) end value = mb:readregisters(123) if value then   dampers_open = getbit(value, 0)   fire_dampers_open = getbit(value, 1)   ... end
Thanks!
(22.12.2016, 10:47)admin Wrote: You can use this helper function:
Its work for read any bit of 16bit register.
i also write any bit of 16bit register this like..
function updatebit(bit_value, ModbusAddress, bit_no)   ????   ????   ???? end
For example;
 updatebit (true, 123, 0)  updatebit (false, 123, 5)
1. --
before modbus 123 register: 1010 1101 0110 1011 (=44.395)
after modbus 123 register: 1010 1101 0110 1010 (=44.394)
2.--
before modbus 123 register: 1010 1101 0110 1010 (=44.394)
after modbus 123 register: 1010 1101 0100 1010 (=44.362)
https://forum.logicmachine.net/showthrea...5#pid11025