modbus energy meter
Hello guys!
Its my first that i integrate with modbus.
Im using an energy meter from legrand ( EMDX3) and i dont receive measurments and when i check the error logs i get this
read failed :Illegal function.
Does ever this happend to anyone else ?
Here is my profile for the device that i builded
.json   legrand_energymeter by MaOP.json (Size: 2.63 KB / Downloads: 10)
You are missing datatype - this will be defined in device manuals. Before making profile use Read test to find correct configuration.
(03.01.2025, 10:29)Daniel Wrote: You are missing datatype - this will be defined in device manuals.  Before making profile use Read test to find correct configuration.
When i try to do it i get Illegal fuction and illegal data value
Do you have manuals with registry definition?
(03.01.2025, 11:09)Daniel Wrote: Do you have manuals with registry definition?
yes , here it is
.pdf   emdx3 multifunction meter modbustable 412045.pdf (Size: 454.17 KB / Downloads: 14)
You have registers, not inputregisters. Try also subtracting register address by 1
(03.01.2025, 11:22)Daniel Wrote: You have registers, not inputregisters. Try also subtracting register address by 1
 I tried Both but unfortunately doesnt work
Try running Read test with the following parameters and post the results.
- Function: Input register (#4)
- Address: 4096
- Data type: uint32
- Read swap: Word (CDAB)
Also try Function = Holding register (#3)
(03.01.2025, 12:21)admin Wrote: Try running Read test with the following parameters and post the results.
- Address: 4096
- Data type: uint32
With holding register i get the volts.. but i dont get the value in the group address.
Try this
"address": 4096, "name": "Voltage L1", "bus_datatype": "float32", "type": "register", "units": "V", "description": "Voltage of phase L1", "datatype": "uint32", "value_multiplier": 0.001
(03.01.2025, 14:18)Daniel Wrote: Try this
it worked, i will do it for all and i will update you
It works perfecty!!!
Thank you gus i will add the profile so if anynone need it to be ready!!
.json   legrand_energymeter EMDX3 tested26.json (Size: 3.34 KB / Downloads: 17)