Bacnet Client port Change
Hi we are using bacnet package not bacnet app for bacnet client function.
We need to change bacnet port from 47808 to 47810. There is a bacnet device in 47810 we found via another bacnetscan app. Can you check the script below for scan device. Also can you share bacnet read command for different port please ?
require('bacnet')
bacnet.port = '0xBAC2'
require('bacnet')
devices = bacnet.scandevices()
log(devices)
Scanning will not work with different port but you can use different port for reading and writing.  Use YABE for scanning.
Example for reading.
require('bacnet') bacnet.port = '0xBAC2' -- read from 192.168.0.21, device id 21 bacnet.deviceip = '192.168.0.21' val1 = bacnet.readvalue(21, 'binary value', 2049) val2 = bacnet.readvalue(21, 'binary value', 2050) val3 = bacnet.readvalue(21, 'binary value', 2051) log(val1, val2, val3)
Hi Daniel,
There are 2 bacnet points. one is bacnet value other is binary input. We read binary value but we can't read binary input. Here is the detailed pictures of the points which are taken from yabe.
What is your script?
Here is the script and logs :
require('bacnet')
bacnet.deviceip = '172.22.22.226'
alarm = bacnet.readvalue(500, 'binary input', 600)
point = bacnet.readvalue(500, 'binary value', 0)
log(alarm , point)
log :
* arg: 1
* nil
* arg: 2
* bool: false
You are changing the port number into a string, use bacnet.port = 0xBAC2 or bacnet.port = 47810
Check the second returned value:
alarm, err = bacnet.readvalue(500, 'binary input', 600) log(alarm, err)
