CANx DALI questions
We have a project where they have installed 80 DALI2 ballasts and 6 DALI2 B.E.G PD4N-BMS sensors.
First and foremost we hate these projects! Why not put up 6 KNX sensors instead!
Anyway, we previously used a KNX/DALI gateway that could control both ballasts and sensors.
If we buy 1x LM5p2-KCD, 2x CAN-DALI-M3, then we can control 30 DALI2 ballast/sensors from each device?
And we need a suitable DALI PSU as well?
We haven't tested BEG sensors but if they adhere to DALI2 standard they should work as any other.
For LM5p2-KCD you need an external DALI power supply like Mean well DLP-04R. For CAN-DALI-M3 you can use standard DC 15V..18V power supply like Mean well HDR-15-15.
Can someone confirm that CAN-DALI-M3 and LM5p2-KCDZ is limited to controlling 30 DALI-2 ballasts/control gear? We are used to our gateways can controll 64 devices per DALI line, so I just want to make sure I have the right information before I proceed with my project.
30 is a recommended limit if internal DALI power supply is used on CAN-DALI-M3. With an external DALI power supply you can use 64 ballasts.
Hi.
As a wish for further updates on the CANx DALI configuration:
- When assigning dali ballasts to groups, it would be a great help to have a "flash" button in the group assigning tab. With this it won't be needed to enter each ballast -> make them blink -> name them and THEN assign them to groups. Instead simply: Assign by flashing and assigning group directly.
I hope it makes sence Smile
(30.10.2025, 08:55)PolymorphedCust Wrote: Hi.
this?
Yes, exactly that !
I'm sorry. I hadn't updated the app, and now the flash (as in your pic) is there, and also the feedback value/switch on each group!
My bad ! Big Grin
(30.10.2025, 10:32)PolymorphedCust Wrote: Yes, exactly that !
My bad ! Big Grin
don't forget to set short address and minimum level of feedback device in group settings to get correct status value in knx
Is there a reason for this? Physical minimum = 85
[Image: 9tdPbdd.png]
(30.10.2025, 13:44)Novodk Wrote: Is there a reason for this? Physical minimum = 85
if you wil set here 100 in minimum level, but in group settings you will set 1 as minimum level, then you wil not get effect in range 1-40 % and 40% wil be minimum value in status
Further question:
If I use only LM5p2-KCD will it be able to handle 64 DALI devices with the 24 VDC supply (as usual)?
Thanks Smile
Yes, but you need an external DALI power supply (Mean Well DLP-04R or any other alternative).
and where should this DALI PSU be connected? I'm thinking of getting the LM5p2-DW1
KCD/KCDZ is a newer device with more features. If you need more DALI lines you can add CANx-DALI gateways to it.
Both KCD and DW1 require an external DALI power supply. Check LM connection diagrams page 6 (DALI): https://logicmachine.net/downloads
OK thanks. But I need the LM5p2-DW1 'cus it has 1-wire as well Smile
What features will I be missing?
Old DALI implementation is very limited - you can only control each ballast separately using on/off and scale objects. Everything else must be done using scripts.
KCD supports DALI groups (control of multiple ballasts), scenes, CCT/RGB/RGBW ballasts. You can change most of ballast parameters directly from the UI. It also supports DALI2 sensors and push-button inputs.
Ok thanks for the info Smile
Hello, have i a LM5Lp can i control dali lights with an external power supply ?? If yes which is the correct wiring diagram ? thank you in advance!!
Page 7
https://logicmachine.net/manuals/lm-conn...260407.pdf
(01.07.2026, 10:32)Daniel Wrote: Page 7
my lm doesnt have the dali connectors so it cant be done right ??