Threads: 35
The usual cause are LM group addresses that are not linked to any KNX devices on the TP bus.
You should either use virtual group addresses or disable "write to bus" option where applicable. In scripts use grp.update/grp.checkupdate for such group addresses.
In general your system looks very healthy.
Threads: 35
Green is when a object receives new telegram, yellow is when object has no name and it was sniffed from the bus. When importing KNX project select: Update existing objects:
If you have another KNX device which is spamming the bus then you can select: ACK all group telegrams in KNX connection settings but it is better to investigate who does it. This will work only for telegrams which are not sent by LM, for telegrams which are sent by LM see my earlier comment.
Threads: 4
thanks, this phrase " You should either use virtual group addresses or disable "write to bus" option where applicable. In scripts use grp.update/grp.checkupdate for such group addresses."
where is "write to bus"? is a group address option in ETS?
Threads: 35
This option you will find when integrating other protocols to LM like modbus/zigbee or in Visu itself.
Nothing to do with ETS.