(03.11.2015, 11:51)admin Wrote: LM conforms to BACnet Application Specific Controller (B-ASC) profile. COV is supported; Schedule, Trend, Alarm and Event are not.
How can I setup the COV's for the LM4? Are these determined by the BACnet-client (reading of the BACnet-objects)?
-espen-
You don't have to configure anything, remote devices subscribe to object COV notifications. There can be 32 active subscriptions.
COV has default delta of 1, for now it can only be changed from BACnet side by other devices. Keep in mind that BACnet service restart or full LM restart will reset COV delta to 1.