Threads: 2
24.08.2017, 13:52
(This post was last modified: 24.08.2017, 13:54 by Demus.)
Hi!
I don't have any experience with Lm. But there is a device on the Modbus to link LM. Please help in creating a profile for the survey of inputs, outputs, and data registers. Map Delta DVP registers and Protocol description for them I've attached.
Thanks in advance for your help in the study of Lm.
Threads: 48
Does it support Modbus RTU? Have you tried communicating with it using RTU read test? From the supplied documentation it seems that PLC uses Modbus ASCII which is not supported by the Modbus mapper.
Threads: 8
24.08.2017, 21:43
(This post was last modified: 24.08.2017, 21:46 by Erwin van der Zwart.)
Delta has there own protocol to a IP gateway, this gateway uploads data to the Delta Cloud Service and there is no API.
What i have done before is reading the Delta gateway's HTTP pages to get the data from it.
It's written for our HVAC SmartStruxure Lite controller, also LUA but it should be easy to port to the LM controller format.
Code: -- ******** Delta Solivia GW -> MPM module version 1.0 created by Erwin van der Zwart ******** 2015-12-10 ******** --
if not init then
-- Import libraries
require ("http")
-- Set timout for max wait time on HTTP response
http.TIMEOUT = 15
-- Delta Solivia GW Settings
IP_Address = '192.168.10.207'
UserName = 'admin'
PassWord = 'Schneider'
-- MPM objects
var("Absolute_Maximum_In_We_Object", "ME.AV44")
var("Percentage_Of_Nominal_Power_Object", "ME.AV45")
-- End init
init = true
-- Login before requesting data
if not login then
response = http.request('http://' .. IP_Address .. '/LoginCgi?ed_user=' .. UserName .. '&pw1=' .. PassWord .. '&logIn=Log+in')
-- Check if Response = successfully completed
for i in string.gmatch(response, '<body><br><h2 align="left"><font color="#339900">.-</font>') do
if i ~= nil then
responsestring = i:match([[color="#339900">(.-)</]])
--print(responsestring)
if responsestring == 'Operation successfully completed!' then
print('Login procedure ready, getting values..')
login = true
-- Get data from webservice
local data = http.request('http://' .. IP_Address .. '/Unbalanced.htm')
--print(data)
-- Check if data is received
if not data then
print('No data found.. , restarting procedure to try again..')
login = nil
return
-- Check if login is handled correct
for i in string.gmatch(data, '<h2>.-</h2>') do
if i ~= nil then
login_asked = i:match([[<h2>(.-)</h2>]])
if login_asked == 'Please log in' then
print('Login not ready or logged out, system will try to login again..')
login = nil
return
-- Power Balancing
for i in string.gmatch(data, '<input type="text".-</p>') do
if i ~= nil then
--print(i)
absolute_maximum_in_We = i:match([[name="t1" value="(.-)"]])
if absolute_maximum_in_We then
Absolute_Maximum_In_We_Object = absolute_maximum_in_We
print('Absolute maximum in We = ' .. absolute_maximum_in_We)
percentage_of_nominal_power = i:match([[name="t2" value="(.-)"]])
if percentage_of_nominal_power then
Percentage_Of_Nominal_Power_Object = percentage_of_nominal_power
print('Percentage of nominal power = ' .. percentage_of_nominal_power)
-- Add extra data pagefields here...
end --End Login
end -- End init
Threads: 2
25.08.2017, 06:19
(This post was last modified: 25.08.2017, 06:26 by Demus.)
(24.08.2017, 17:42)admin Wrote: Does it support Modbus RTU? Have you tried communicating with it using RTU read test? From the supplied documentation it seems that PLC uses Modbus ASCII which is not supported by the Modbus mapper.
Yes, Modbus rtu is supported. He included me in the PLC. Test to read from register LM is successful. I have difficulties to describe the profile line to read for example the register D0 at the address 4096.
With this option the register is not read. Don't understand what the problem is.
{ "name": "Input 1", "bus_datatype": "float16", "type": "inputregister", "address": 4096, "value_multiplier": 0.001, "units": "V" },
{ "name": "Input 2", "bus_datatype": "float16", "type": "inputregister", "address": 4096, "value_multiplier": 0.001, "units": "V" },
(24.08.2017, 21:43)Erwin van der Zwart Wrote: Hi,
if not init then
-- Import libraries
require ("http")
http.TIMEOUT = 15
UserName = 'admin'
-- MPM objects
-- End init
init = true
if not login then
if i ~= nil then
login = true
--print(data)
if not data then
login = nil
return
if i ~= nil then
login = nil
return
-- Power Balancing
if i ~= nil then
--print(i)
end --End Login
end -- End init
I think you are on the other controllers speak. I'm working with this on rs-485.
http://www.deltaww.com/Products/Category...2%20Series
Threads: 48
Try changing type to "register"
Threads: 2
25.08.2017, 06:56
(This post was last modified: 25.08.2017, 07:07 by Demus.)
(25.08.2017, 06:49)admin Wrote: Try changing type to "register"
Thank you very much! Works!
One more question. Can I one and the same port to use for the survey using a script and using the profile? Devices are polled different.
Threads: 48
Yes, but modbus proxy functions must be used, see this post for more info: https://forum.logicmachine.net/showthrea...53#pid1953