CoolAutomation - CoolMasterNet integration
CoolMasterNet device uses TCP instead of RS-232 for communication, so we've updated the script to work with IP.
1. Create a resident script with 0 sleep interval, change 192.168.3.20 to CoolMasterNet device IP. Status information is polled every 3 seconds.
2. Create objects:
All objects must have VRV tag set.
Set object names, using the following scheme (full address and function):
L1.101 on/off - 1-bit, unit on/off control
L1.101 setpoint - unit setpoint, 2-byte floating point
L1.101 mode - unit mode, 1-byte (0 = cool, 1 = heat, 2 = fan, 3 = dry, 4 = auto)
L1.101 fspeed - fan speed, 1-byte (0 = low, 1 = medium, 2 = high, 3 = top, 4 = auto)
L1 on/off - 1-bit, on/off control for all units on a given line
L* on/off - 1-bit, on/off control for all units on all lines
You can create status objects by adding "status" to object name, example:
L1.101 on/off status
L1.101 setpoint status
L1.101 mode status
L1.101 fspeed status
L1.101 temp status - room temperature, 2-byte floating point
if not client then
  require('socket')
  IP = '192.168.3.20'
  PORT = 10102
  -- knx <> coolmaster mapping
  knxtocm = {}
  cmtoknx = {}
  function reverse(src)
    local res = {}
    for k, v in ipairs(src) do
      res[ v ] = k - 1
    return res
  -- integer<>text mode/fspeed value mapping
  modetotext = { 'cool', 'heat', 'fan', 'dry', 'auto' }
  texttomode = reverse(modetotext)
  speedtotext = { 'low', 'med', 'high', 'top', 'auto' }
  texttospeed = reverse(speedtotext)
  -- get all tagged objects and set mapping
  for _, object in ipairs(grp.tag('VRV')) do
    local address, fn, stat = unpack(object.name:split(' '))
    -- status object
    if stat then
      if not cmtoknx[ address ] then
        cmtoknx[ address ] = {}
      cmtoknx[ address ][ fn ] = {
        id = object.id,
        value = grp.getvalue(object.id),
    -- control object
      knxtocm[ object.id ] = {
        address = address,
        fn = fn,
  function checkerror(res, err)
    if not res then
      sock:close()
      sock = nil
      alert('CoolMaster error: %s', tostring(err))
    return res, err
  function connect()
    sock = socket.tcp()
    sock:settimeout(5)
    return checkerror(sock:connect(IP, PORT))
  function send(data)
    if not sock then
      connect()
    if sock then
      checkerror(sock:send(data))
  -- read single line from socket
  function readline()
    if not sock then
      connect()
    if sock then
      return checkerror(sock:receive())
  function updateknx(address, fn, value, datatype)
    local object = cmtoknx[ address ] and cmtoknx[ address ][ fn ] or nil
    -- object not found
    if not object then
      return
    -- no value or same value, no update required
    if value == nil or object.value == value then
      return
    -- save new value and write to knx
    object.value = value
    grp.write(object.id, value, datatype)
  function parseline(line)
    local address, status, setpoint, temp, speed, mode
    line = line:gsub('>', '')
    address = line:sub(1, 6)
    -- address is invalid, cannot parse line
    if address:sub(1, 1) ~= 'L' then
      return
    -- on/off status
    status = line:sub(8, 9):lower() == 'on'
    updateknx(address, 'on/off', status, dt.bool)
    -- setpoint is integer
    setpoint = line:sub(12, 13)
    setpoint = tonumber(setpoint)
    updateknx(address, 'setpoint', setpoint, dt.float16)
    -- room temp is float, separated by comma
    temp = line:sub(16, 17)
    temp = tonumber(temp)
    updateknx(address, 'temp', temp, dt.float16)
    -- speed: low, med, high, auto
    speed = line:sub(20, 23):lower():trim()
    updateknx(address, 'fspeed', texttospeed[ speed ], dt.uint8)
    -- mode: cool, heat, fan, dry, auto
    mode = line:sub(25, 28):lower():trim()
    updateknx(address, 'mode', texttomode[ mode ], dt.uint8)
  -- read current status
  function readstat()
    send('ls\r\n')
    -- read until error or end of stat
    while true do
      local line = readline()
      -- timeout or end occured
      if not line or line == 'OK' then
        break
      parseline(line)
  -- handle group writes
  function eventhandler(event)
    local object, cmd, value, param
    object = knxtocm[ event.dstraw ]
    -- knx object not mapped, ignore
    if not object then
      return
    -- on/off - boolean
    if object.fn == 'on/off' then
      value = knxdatatype.decode(event.datahex, dt.bool)
      cmd = value and 'on' or 'off'
    -- setpoint - floating point
    elseif object.fn == 'setpoint' then
      value = knxdatatype.decode(event.datahex, dt.float16)
      param = string.format('%.1f', value)
      cmd = 'temp'
    -- mode (fan, dry, auto)
    elseif object.fn == 'mode' then
      value = knxdatatype.decode(event.datahex, dt.uint8)
      cmd = modetotext[ value + 1 ]
    -- speed (low, medium, high, auto)
    elseif object.fn == 'fspeed' then
      param = speedtotext[ value + 1 ]
      if param then
        cmd = 'fspeed'
    -- got valid command
    if cmd then
      -- append address to command
      cmd = cmd .. ' ' .. object.address
      -- append additional parameter if set
      if param then
        cmd = cmd .. ' ' .. param
      send(cmd .. '\r\n')
      readline() -- command result
  -- knx connection
  client = eibdgm:new({ timeout = 1 })
  client:sethandler('groupwrite', eventhandler)
  -- start-up time
  sec, usec = os.microtime()
-- handle knx
client:step()
-- read stats every 3 seconds
diff = os.udifftime(sec, usec)
if diff < 0 or diff >= 3 then
  readstat()
Hello!
I need some assistance/direction with a Lua script, please.
I have installed a Clipsal 5500SHAC:
https://www.clipsal.com/products/detail?...cument-1=0
I have installed a CoolMasterNet to integrate with the Daikin VRV system. The CoolMasterNet has been configured and is working correctly. It is connected via IP.
https://coolautomation.com/news/c-bus-by...-hvac-vrf/
I need some assistance with the Lua script, please?
Thank you!
Torstein.
This script was created for LM,W4k,SL it will not work for NAC as they have different functions to write to objects. It require a bit of modifications.
in NAC Keywoards = TAG
(25.06.2020, 07:47)Daniel. Wrote: This script was created for LM,W4k,SL it will not work for NAC as they have different functions to write to objects.  It require a bit of modifications.
Thanks Daniel! Is there any way I can arrange for the required modifications to be done?
Thanks,
T.