This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

Spacelynk and Exiway Smart control
#1
Hi 
 
I'm testing the AN049 Exiway smart control with Spacelynk.
All communications are running and I get the feedback from the emergency lights.

But in the Spacelynk all objects are numbers, and in the docs each bit have their own explanation in each register.
Have anyone (Erwin? Smile ) already made scripts for extracting this bit's (correct) in the different registers???

And I'm struggling to find explanation for all the bits in the registers.

Hope someone could give me hand on this one.
Have tried using some of the other scripts on this forum, but when I don't know what all the bits stands for, it's always a 
possibility that the bitshift or something's not correct.

Eirik
Reply
#2
Hi,

Sorry we don’t use Exiway in the Netherlands, so i have nothing on script here..

We could help you out if we have more info on the challange you are facing.

BR,

Erwin
Reply
#3
Hi
I wrote to SE support and they should get in touch with you.
BR
------------------------------
Ctrl+F5
Reply
#4
Hi 

Been testing this at the office and got this to work.
Used this to decode the bits:
Code:
function getbit(value, nr)
 value = bit.rshift(value, nr)
 return bit.band(value, 1) == 1
end

value = event.getvalue()

grp.checkupdate('32/5/1', getbit(value, 0))
grp.checkupdate('32/5/2', getbit(value, 1))
grp.checkupdate('32/5/3', getbit(value, 2))
grp.checkupdate('32/5/4', getbit(value, 3))
grp.checkupdate('32/5/5', getbit(value, 4))
grp.checkupdate('32/5/6', getbit(value, 5))
grp.checkupdate('32/5/7', getbit(value, 6))
grp.checkupdate('32/5/8', getbit(value, 7))
Runs as Event based script in each register.
Works like a charm.
This is the result.
   

The objects called "dummy_something" is bits not explained in the application note.
Its the only thing I can't figure out.