This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

LM5 polling rate KNX
#10
(18.12.2018, 11:36)admin Wrote: Keep in mind that with 1000 objects and 1 second delay each object will be polled once in 17 minutes. The question is why do you need polling instead of devices sending object values on change and/or by their own timer?

Because all devices doesnt have cyclic sending for all objects, and the BMS does not support polling trough KNX protocol. Thats why we poll via LM5. BMS turns on their updateflag so that values get updated in the BMS, for example after restart or crash.