I have connected a PT1000 to the device, and it is sending 154.88ºC, does the PT100/PT1000-KNX auto-detects if there is a PT100 or a PT1000 connected? or do I have to upload a different KNX database?.
Tested the probes and the resistance is between 107 to 120º when heated with the hands...
also, I've connected several resistors directly to the device (from 100 to 1200 ohm), and it returns values of the sort.. 86,8º, 213º, etc..
Tested the probes and the resistance is between 107 to 120º when heated with the hands...
also, I've connected several resistors directly to the device (from 100 to 1200 ohm), and it returns values of the sort.. 86,8º, 213º, etc..