09.01.2019, 20:26
(08.01.2019, 08:42)Daniel. Wrote: Hi
Check if your thermostat send the setpoint value to the bus once changed manually.
BR
Hi,
Yes it sends the value once it is changed manually. The problems that occurs is that the actual setpoint differences with 1-3 degrees unlike the setpoint input, and it stays this way even if i set a new setpoint through LM5 vizulasation. For exempel if i set 19 degrees the actual setpoint become 21, and if i set 25 the actual setpoint become 27 and so on. The thermostat regulates after the actual setpoint value and not the setpoint written.
This is not a problem until someone operate the thermostate manually after program transfer. The input and actual setpoint stays the same when just operated by the LM5... Could it be some setting in the thermostat that is causing this?