This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

BACnet - How many points
#3
Hi,

Wiser for KNX has a software limit to 150 points, spaceLYnk is just like LM without restrictions.

We run tests in our lab to determine the recommended number of BACnet objects and we just finalized the HW3 tests. Here are the results:

There is recommended limit for 500 objects exportable to BACnet for HW1 in the user guide which can be reviewed based on this test report. The HW3 can handle up to 2000 object with respect to other running processes, activities and assuming that there is not traffic on KNX bus. When KNX traffic is present the limits must be modified accordingly.

BR,

Erwin
Reply


Messages In This Thread
BACnet - How many points - by chriscroko - 23.01.2019, 10:06
RE: BACnet - How many points - by admin - 23.01.2019, 10:28
RE: BACnet - How many points - by Erwin van der Zwart - 23.01.2019, 20:12
RE: BACnet - How many points - by chriscroko - 25.01.2019, 05:34

Forum Jump: