This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm that you accept these cookies being set.

KNX to Modbus TCP/IP
#1
Hi

Trying to integrate a Trox X Aircontrol with a LM5 and KNX. Our goal is to use the values on KNX and send them to the Trox unit, from KNX to Modbus TCP/IP. We are going to do it in 10 zones, but starting with zone 1. The three values are actual temperatur, actual setpoint and actual ppm value.

I think we tried all sorts of datatypes, all sorts of types and addresses and writable false or true.

Code:
{
"manufacturer": "Trox",
"description": "Test",

"mapping": [
{ "name": "Ertemp Zone 1", "bus_datatype": "float", "type": "register", "address": 1009, "datatype": "float32", "value_multiplier":0.1, "writable": false  },
{ "name": "CO2", "bus_datatype": "float", "type": "register", "address": 1012, "datatype": "float32", "writable": false  },
{ "name": "Setpoint", "bus_datatype": "float", "type": "register", "address": 1014, "datatype": "float64", "value_multiplier":0.1, "writable": false  }

]
}



Any ideas how it should be?

Attached Files
.pdf   X-AIRCONTROL_Modbus_Protokol_GB.pdf (Size: 1.39 MB / Downloads: 12)
Reply


Messages In This Thread
KNX to Modbus TCP/IP - by Rune - 19.02.2019, 13:54
RE: KNX to Modbus TCP/IP - by admin - 20.02.2019, 07:34
RE: KNX to Modbus TCP/IP - by Rune - 20.02.2019, 14:38